GEK-106310AB F650 Digital Bay Controller 5-51
5 SETTINGS 5.4 PROTECTION ELEMENTS
5
Table 5–43: BLOCK AND OPERATION SIGNALS FOR THE PHASE DIRECTIONAL ELEMENT
Signals provided by the directional element are, block and operation signals. Signals used to block overcurrent elements
are configured at Setpoint > Relay Configuration > Protection Elements.
Operation signals are active when operation and polarization magnitudes meet conditions given by the settings.
Block signals indicate blocked elements by an external block input or by polarization voltage loss. Using the “Block logic”
setting, the user can select how the directional element responds in case of a block. When the “Block” option is selected,
the operational signal will not be activated in a block condition. When the “Permission” option is selected, the operation
signal will be activated in a block condition.
Figure 5–8: shows the default configuration for the phase overcurrent block input. When the “Block logic” setting is set as
“Block”, this input will be active in case of a block in the directional element, avoiding any phase overcurrent trip.
When the “Block logic” setting is set as “Permission”, the phase overcurrent element is enabled to trip as the block input is
not active in case of polarization voltage loss.
BLOCK AND OPERATION FOR 67P
PHASE DIR1 BLOCK A
PHASE DIR1 A OP
PHASE DIR1 BLOCK B
PHASE DIR1 B OP
PHASE DIR1 BLOCK C
PHASE DIR1 C OP
PHASE DIR2 BLOCK A
PHASE DIR2 A OP
PHASE DIR2 BLOCK B
PHASE DIR2 B OP
PHASE DIR2 BLOCK C
PHASE DIR2 C OP
PHASE DIR3 BLOCK A
PHASE DIR3 A OP
PHASE DIR3 BLOCK B
PHASE DIR3 B OP
PHASE DIR3 BLOCK C
PHASE DIR3 C OP