5-136 F650 Digital Bay Controller GEK-106310AB
5.7 REMOTE COMMS 5 SETTINGS
5
5.7REMOTE COMMS
This settings allow configuring the remote comms settings for the IEC61850 protocol regarding GSSE. For more
information see chapter 7.1.1 REMOTE DEVICES.
SETPOINT > INPUTS/OUTPUTS > REMOTE COMMS
SETTING DESCRIPTION NAME DEFAULT VALUE STEP RANGE
Remote comms selection Remote Comms NONE N/A [NONE – GSSE – GOOSE]
SETTING DESCRIPTION FOR GSSE
Remote comms selection Remote Comms GSSE N/A [NONE – GSSE – GOOSE]
Device Identification 650 ID F650 N/A
Hold time signal send by the
transmitting device
Hold Time 10000 1 ms [1000 : 60000]
Snapshot Events Generation Snapshot Events Remote Out DISABLED N/A [DISABLED – ENABLED]
Remote Device Description Remote Device X Remote Device X N/A
Bit Pair Selection Bit Pair X None N/A [DNA-1 to DNA-32 –
UserSt-1 to UserSt-64]
Default Value Selection Default Value X OFF N/A [OFF – ON – LATEST OFF
– LATEST ON]
SETTING DESCRIPTION FOR GOOSE
Remote comms selection Remote Comms GOOSE N/A [NONE – GSSE – GOOSE]
Default Value Selection Default Value X OFF N/A [OFF – ON – LATEST OFF
– LATEST ON]
Note: X is the Remote Device index, up to 32

Table of Contents

Other manuals for GE F650

Questions and Answers:

Question and Answer IconNeed help?

Do you have a question about the GE F650 and is the answer not in the manual?

GE F650 Specifications

General IconGeneral
ModelF650
CategoryController
Frequency50/60 Hz
DisplayLCD
TypeFeeder Protection Relay
ApplicationFeeder Protection and Control
Communication ProtocolsDNP3, Modbus, IEC 61850
Protection FunctionsOvercurrent, Earth Fault
ManufacturerGeneral Electric
Input Voltage24-250 VDC/VAC

Related product manuals