GEK-106310AB F650 Digital Bay Controller 5-151
5 SETTINGS 5.9 RELAY CONFIGURATION
5
Table 5–111: ACTIVE SYMBOLS CONFIGURABLE IN ONE-LINE DIAGRAM FOR GRAPHICAL HMI
ACTIVE SYMBOLS
ICONS IN SCREEN DESCRIPTION
SWITCHGEAR SYMBOLS STANDARD AND IEC 1082-1 SWITCHGEAR SYMBOLS
STANDARD SWITCHGEAR SYMBOLS M and C selection for graphic display option in the ordering code
These symbols correspond to switchgear elements: breaker (square) and
selector switch (rhombus), in vertical and horizontal positions. It is necessary
to associate the figure to its corresponding switchgear number. The figure is
shown filled if the element is closed, and blank if the element is open. The
symbol on the right represents an unpluggable breaker. In this case it is
necessary to indicate which operands show whether the element is plugged or
unplugged. The figure shows also graphically these two statuses.
IEC SWITCHGEAR SYMBOLS N and C selection for graphic display option in the ordering code
These symbols correspond to breakers and. breaker trucks in vertical and
horizontal positions. The first fourth symbols are breakers in vertical and
horizontal positions for left and right options. The last fourth symbols are
breaker trucks or unpluggable breakers. When the device is connected two
arrows can be seen, if the device is not connected only one arrow is displayed.
When the device it is inserted the device can be seen and when it is not
inserted only a blank space will be displayed
These symbols correspond to contactors in vertical and horizontal positions
These symbols correspond to selector switches in vertical and horizontal
positions.
OTHER CONFIGURABLE SYMBOLS Available for both M, N, C and D selection
MULTISTATE VARIABLE SYMBOL
Displays on screen a dialog box that is one variable status function (like a
switch case) for the following internal states AR STATUS, AR LOCKOUT
MODE, AR BLOCK MODE and FAULT TYPE.
This type of data allows to visualize the different states of one particular value,
for example, AR STATUS has several states such as (0) OUT OF SERVICE,
(1) READY, (2) LOCKOUT, (3) BLOCK, (4) RECLOSE IN PROGRESS.
Significant texts can be associated with those states.
STATUS SYMBOLS (TEXT AND GRAPHIC MODES):
Bit: Represents the state of an operand by means of a configurable text. It
allows associating a test to the active status and a different text to the inactive
status.
Led(O) Performs the same function in a graphical mode. This way, it works as
a virtual LED. When showing a black circle, it means that the selected operand
is active, and if the circle is blank, the operand is inactive
ANALOG MAGNITUDE SYMBOL
Used for displaying analog magnitudes (current, voltage, power, etc.) in
floating point numbers, such as a current value (123.5 A). Both the number of
decimals and the integer characters can be selected, in order to facilitate the
reading. Any of the analog magnitudes available in the relay can be
configured.