GEK-106310AB F650 Digital Bay Controller 7-37
7 IEC 61850 PROTOCOL 7.2 IEC 61850 PROFILE FOR F650
7
2.3.2 RREC (Autoreclosing)
This logical node class is used for autorecloser and has 1 instance inside the device.
Notes:
AutoRecSt object includes extra enum values specified by Tissue 3 and Tissue 133 (See the Enum types implementation
section) .
ACT includes origin attribute in ST, this is implemented according to Tissue 68.
RREC class
Attribute
Name
Attribute
Type
Explanation M/O/E Notes
RREC Autoreclosing
Data
Common Logical Node Information
Mod INC Mode M Status-only
Beh INS Behaviour M
Health INS Health M
Status Information
Op ACT Operate M AR Close Breaker
AutoRecSt INS Auto Reclosing status M AR Status
AutoRecLo INS Auto Reclosing Lockout Status E AR Lockout Mode
AutoRecBlk INS Auto Reclosing Block Status E AR Block Mode
Settings
Rec1Tmms ING First Reclose Time O Dead Time 1
Units in miliseconds
Rec2Tmms ING Second Reclose Time O Dead Time 2
Units in miliseconds
Rec3Tmms ING Third Reclose Time O Dead Time 3
Units in miliseconds
Rec4Tmms ING Fourth Reclose Time E Dead Time 4
Units in miliseconds
RclTmms ING Reclaim Time O Reclaim Time
Units in miliseconds
MaxNumShot ING Max number of Shots E Max number Shots
RsTmms ASG Reclosing --> Ready E Reset Time
HoldTmms ASG Cond Check Time E Hold Time
CondEna SPG Check Cond (Enable, Disable) E Cond Permission
RRECEna SPG Function Enable, Disable E Function Permission