7-58 F650 Digital Bay Controller GEK-106310AB
7.2 IEC 61850 PROFILE FOR F650 7 IEC 61850 PROTOCOL
7
Description(cont.) Value / Clarification(cont.)
What service error types are supported Y instance-not-available
Y instance-in-use
Y access-violation
Y access-not-allowed-in-current-state
Y parameter-value-inappropriate
Y parameter-value-inconsistent
Y class-not-supported
Y instance-locked-by-other-client
Y control-must-be-selected
Y type-conflict
Y failed-due-to-communications-constraint
Y failed-due-to-server-constraint
What additional cause diagnosis are supported N Unknown
Y Not-supported
N Blocked-by-switching-hierarchy
N Select-failed
Y Invalid-position
Y Position-reached
N Parameter-change-in-execution
N Step-limit
N Blocked-by-Mode
N Blocked-by-process
N Blocked-by-interlocking
N Blocked-by-synchrocheck
Y Command-already-in-execution
N Blocked-by-health
N 1-of-n-control
N Abortion-by-cancel
Y Time-limit-over
N Abortion-by-trip
Y Object-not-selected
How to force a “test-not-ok” respond with SelectWithValue
request?
Not applicable.
How to force a “test-not-ok” respond with Operate
request?
Not applicable.
Which origin categories are supported? What happens if
the orCat is not supported?
orCat values are checked only for XCBR1$CO$Pos. The
permision to do the operation depends on the position of
LOCAL/REMOTE switch on the front panel of relay and
also on the orCat value received. The following table shows
the behaviour. “Yes” means operation is permitted “No”
means operation is not permitted.
OrCat
2,3,5,6
When invalid orCat is received or LOCAL/REMOTE switch
is in LOCAL position then DUT will respond with negative
value OBJECT-ACCESS-DENIED. Additionally in case of
Direct Control with Enhanced Scurity or SBO with
Enhanced Scurity when invalid orCat is received the DUT
will send InformationReport with AddCause = not-
supported.
Does the IED accept an select/operate with the same
ctlVal as the current status value?
Select: Y
Operate : N
Does the IED accept a select/operate on the same control
object from 2 different clients at the same time?
Select: N
Operate : N for SBO, SBO Enhanced
Operate: Y for Direct-Control and Direct-Control Enhanced.
However in case of Direct-Control with Enhanced Security
as long as the control object has not returned to state
Ready the Operate request from the second client will be
rejected.