GEK-106310AB F650 Digital Bay Controller 11-7
11 APPLICATION EXAMPLES 11.2 EXAMPLE 2: TOC PROTECTION + RECLOSING SETTINGS PROCEDURE
11
The F650 trip contact over-travel is the time the contact remains closed for some definite time to assure the tripping action
of the breaker, specially in CB’s with large tripping times (bulk or other CB’s). This time delay has been set in group
SETPOINT  CONTROL ELEMENTS  INPUTS/OUTPUTS  BOARD F
To test the reclosing scheme one current and two voltages signals equipment with phase and frequency shifting capability
must be used. The current source must be switched OFF and ON in the time ranges described in the scheme
Figure 11–1: F650 TRIPPING AND RECLOSING SCHEME

Table of Contents

Other manuals for GE F650

Questions and Answers:

Question and Answer IconNeed help?

Do you have a question about the GE F650 and is the answer not in the manual?

GE F650 Specifications

General IconGeneral
ModelF650
CategoryController
Frequency50/60 Hz
DisplayLCD
TypeFeeder Protection Relay
ApplicationFeeder Protection and Control
Communication ProtocolsDNP3, Modbus, IEC 61850
Protection FunctionsOvercurrent, Earth Fault
ManufacturerGeneral Electric
Input Voltage24-250 VDC/VAC