GEK-106310AB F650 Digital Bay Controller B-87
APPENDIX B B.7 MEMORY MAP
B
Ajustes Subtensión Auxiliar Grupo 1 - Auxiliary UV 1 Settings
0x282E Function F012 1 R/W 1 0=DISABLED
1=ENABLED
0x282F Pickup Level F003 1 R/W 2 [3 , 300] V
0x2831 Curve F012 1 R/W 1 0=DEFINITE TIME
1=INVERSE TIME
0x2832 Delay F003 1 R/W 2 [0.00 , 900.00] s
0x2834 Snapshot Events F012 1 R/W 1 0=DISABLED
1=ENABLED
0x2847 Confirmation address W 1
Ajustes Subtensión Auxiliar Grupo 2 - Auxiliary UV 2 Settings
0x2848 Function F012 1 R/W 1 0=DISABLED
1=ENABLED
0x2849 Pickup Level F003 1 R/W 2 [3 , 300] V
0x284B Curve F012 1 R/W 1 0=DEFINITE TIME
1=INVERSE TIME
0x284C Delay F003 1 R/W 2 [0.00 , 900.00] s
0x284E Snapshot Events F012 1 R/W 1 0=DISABLED
1=ENABLED
0x2861 Confirmation address W 1
Ajustes Subtensión Auxiliar Grupo 3 - Auxiliary UV 3 Settings
0x2862 Function F012 1 R/W 1 0=DISABLED
1=ENABLED
0x2863 Pickup Level F003 1 R/W 2 [3 , 300] V
0x2865 Curve F012 1 R/W 1 0=DEFINITE TIME
1=INVERSE TIME
0x2866 Delay F003 1 R/W 2 [0.00 , 900.00] s
0x2868 Snapshot Events F012 1 R/W 1 0=DISABLED
1=ENABLED
0x287B Confirmation address W 1
Ajustes Sobretensión de Fases Grupo 1 - Phase OV 1 Settings
0x287C Function F012 1 R/W 1 0=DISABLED
1=ENABLED
0x287D Pickup Level F003 1 R/W 2 [3 , 300] V
0x287F Trip Delay F003 1 R/W 2 [0.00 , 900.00] s
0x2881 Reset Delay F003 1 R/W 2 [0.00 , 900.00] s
0x2883 Logic F012 1 R/W 1 0=ANY PHASE
1=TWO PHASES
2=ALL PHASES
0x2884 Snapshot Events F012 1 R/W 1 0=DISABLED
1=ENABLED
0x2897 Confirmation address W 1
ADDRESS BIT NAME FORMAT STEP MODE LENGTH MISCELLANEOUS