GEK-106310AB F650 Digital Bay Controller B-135
APPENDIX B B.7 MEMORY MAP
B
Inversión de carga 3-Load Encroachment 3
0x41CE Function F012 1,000 R/W 1 0=DISABLED
1=ENABLED
0x41CF Min. Voltage F003 1,000 R/W 2 [0.00 , 300.00] V
0x41D1 Reach F003 1,000 R/W 2 [0.02 , 250.00] Ohm
0x41D3 Angle F003 1,000 R/W 2 [5 , 50] Deg
0x41D5 Pickup Delay F003 1,000 R/W 2 [0.000 , 65.535] s
0x41D7 Reset Delay F003 1,000 R/W 2 [0.000 , 65.535] s
0x41D9 Snapshot Events F012 1,000 R/W 1 0=DISABLED
1=ENABLED
0x41EC Confirmation address W 1
Ajustes Protocolo PROCOME - PROCOME Protocol Communication Settings
0x420A COMM Port F012 1 R/W 1 0=NONE
1=COM 1
0x420B Slave Number F004 1 R/W 1 [0 , 254]
0x4210 Confirmation address W 1
32N1 High - wattmetric Ground Fault High Level Group 1 Settings
0x44A0 Function F012 1 R/W 1 0=DISABLED
1=ENABLED
0x44A1 Voltage Pickup Level F003 1 R/W 2 [2.00 , 70.00] V
0x44A3 Current Selection F012 1 R/W 1 0=IN
1=IG
0x44A4 OC Pickup Level F003 1 R/W 2 [0.005 , 0.400] A
0x44A6 OC Pickup Delay F003 1 R/W 2 [0.00 , 600.00] s
0x44A8 Power Pickup F003 1 R/W 2 [0.01 , 4.50] W
0x44AA MTA F004 1 R/W 1 [0 , 360] Deg
0x44AB Power Pickup Delay F003 1 R/W 2 [0.00 , 600.00] s
0x44AD Curve F012 1 R/W 1 0=DEFINITE TIME
1=INVERSE TIME
2=USER CURVE A
3=USER CURVE B
4=USER CURVE C
5=USER CURVE D
0x44AE Multiplier F003 1 R/W 2 [0.02 , 2.00] s
0x44B0 Snapshot Events F012 1 R/W 1 0=DISABLED
1=ENABLED
0x44BA Confirmation address W 1
32N2 High - wattmetric Ground Fault High Level Group 2 Settings
0x44BB Function F012 1 R/W 1 0=DISABLED
1=ENABLED
0x44BC Voltage Pickup Level F003 1 R/W 2 [2.00 , 70.00] V
0x44BE Current Selection F012 1 R/W 1 0=IN
1=IG
0x44BF OC Pickup Level F003 1 R/W 2 [0.005 , 0.400] A
0x44C1 OC Pickup Delay F003 1 R/W 2 [0.00 , 600.00] s
0x44C3 Power Pickup F003 1 R/W 2 [0.01 , 4.50] W
0x44C5 MTA F004 1 R/W 1 [0 , 360] Deg
0x44C6 Power Pickup Delay F003 1 R/W 2 [0.00 , 600.00] s
0x44C8 Curve F012 1 R/W 1 0=DEFINITE TIME
1=INVERSE TIME
ADDRESS BIT NAME FORMAT STEP MODE LENGTH MISCELLANEOUS