Return to Table of Contents Electrical System Repair Instructions Page 7-23
Load Operation Modes
Table 7-2. Load Operation Modes
LOAD
COOLING MODE
OFF MODE
DEFROST MODE
Compressor
Energized
De-Energized
De-Energized
Condenser Fan
Energized
De-Energized
De-Energized
Evaporator Fan
Energized
Energized
Energized
Mullion Heaters
Energized
Energized
Energized
Eliwell Controller Display
No icon illuminated
Dixell Controller Display
No icon illuminated
Inverter (if applicable)
Energized
De-Energized
De-Energized
Electronic Controller
Note: The digital readout is monitoring true air
temperature, not product temperature.
Table 7-3. Controller Where-Used Table
Controller Type
Build Date
Eliwell
Beginning 9/19/2016
Dixell
4/1/2013 to 9/16/2016
Eliwell Controller
Press and release controller set key to display
‘Machine Status’ menu and ‘SEt’ label.
Press and release the set key again to display the
current set point.
Refer to Table 7-4 for factory set point.
To adjust controller set point, press up and down
arrow keys within 15 seconds.
Press set key once for controller to memorize new
set point.
Be sure to allow 24 hours between temperature
controller adjustments.
Dixell Controller
To view set point, press and release SET key.
Refer to Table 7-4 for factory set point.
To change set point value, press and hold SET key
for at least 2 seconds. The set point value will be
displayed along with a blinking “°C” or “°F” LED.
Release the SET key and then use up or down
arrows within 10 seconds to change the set point.
The new set point will be memorized by either
pressing SET key again or by waiting 10 seconds.