Programming 10
2:DCInj to Stop: When the Run command is removed, the Drive will Baseblock (turn off its output) for the Minimum Baseblock
Time (L2-03). Once the Minimum Baseblock Time has expired, the Drive will inject DC current into the motor windings to lock the
motor shaft. The stopping time will be reduced as compared to Coast to Stop. The level of DC Injection current is set by parameter
b2-02 (50% Default). The DC Injection brake time is determined by the set value in b2-04 and the output frequency at the time the
Run command is removed.
Fig. 6 DC Injection Braking to Stop
3:Coast w/Timer: When the Run command is removed, the Drive will turn off its output and the motor will coast to a stop. If a
Run command is input before time T (value of C1-02) expires, the Drive will not run and the Run command will need to be
cycled before operation can occur. The time T (value of C1-02) is determined by the output frequency when the Run command
is removed and the active deceleration time.
Fig. 7 Coast to Stop with Timer
IMPORTANT
If an overcurrent (OC) fault occurs during DCInj to Stop, lengthen the Minimum Baseblock Time (L2-03)
until the fault no longer occurs.
04)-(E1Frequency Maximum
FrequencyOutput 1004)-(b2
Time BrakeInjection DC
××
=
ON
OFF
Run Command
Output Frequency
Drive Output Voltage Interrupted
DC Injection Brake
DC Injection Brake Time
Minimum Baseblock
Time (L2-03)
100 %
0 %
DC Injection Brake Time
b2-04 x 10
b2-04
10%
100% (Maximum
Output Frequency)
b2-04
(CLOSED)
(OPEN)
Run Command
Output Frequency
Drive Output
Voltage
Interrupted
OFF
ON
Timer Value T
(C1-02)
100 %
0 %
Operation Wait Time (T)
Deceleration
Time (C1-02)
Minimum
Baseblock
Time (L2-03)
Minimum
Output
Frequency
100% (Maximum
Output
Frequency)
Output Frequency at Stop Command Input
Ignored
Run Command
Timer Value T
(C1-02)
(OPEN)
(CLOSED)

Other manuals for YASKAWA F7

Questions and Answers:

Question and Answer IconNeed help?

Do you have a question about the YASKAWA F7 and is the answer not in the manual?

YASKAWA F7 Specifications

General IconGeneral
SeriesF7
TypeDC Drive
FeedbackTachometer, Encoder
CommunicationRS-485, DeviceNet, Profibus, Modbus
Protection FeaturesOvercurrent, Overvoltage, Undervoltage, Overheating, Short Circuit
Storage Temperature-20°C to +70°C (-4°F to 158°F)
Humidity95% RH or less (non-condensing)
Enclosure RatingIP20
Input Voltage200-240V AC, 380-480V AC

Related product manuals