iv
Drive Output Specifications
The standard Drive specifications are listed in the following tables.
208-240Vac
Table i.2 208-240Vac Drive Specifications
208-240Vac 208-230Vac
Model Number CIMR-F7U
20P4 20P7 21P5 22P2 23P7 25P5 27P5 2011 2015 2018 2022 2030 2037 2045 2055 2075 2090 2110
Rated output
capacity
(kVA)
1.2 1.6 2.7 3.7 5.7 8.8 12.0 17.0 22.0 27.0 32.0 44.0 55.0 69.0 82.0 110.0 130.0
N/A
Horsepower
*2
0.5/0.75 2 2 3 5 7.5 10 15 20 25 30 40 50 60 75 100 125
Rated output
current
(A)
3.2 4.2 7.0 9.6 15.2 23.0 31.0 45.0 58.0 71 85.0 115.0 145.0 180.0 215 283.0 346.0
Overload capacity
*3
(% of rated output
current for 60 sec.)
150
Current limit (% of
rated output current)
150
Carrier frequency
*4
2kHz
Maximum output
frequency
300.0Hz
Rated output
capacity
(kVA)
1.4 1.8 3.0 4.1 6.4 8.8 12.0 18.0 23.0 29.0 34.0 44.0 62.0 73.0 82.0 120.0 140.0 160.0
Horsepower
*2
0.5/0.75 1 2 3 5 7.5 10 15 20 25 30 40 50/60 75 75 100/125 150 150
Rated output
current
(A)
3.6 4.6 7.8 10.8 16.8 23.0 31.0 46.2 59.4 74.8 88.0 115.0 162.0 192.0 215 312.0 360.0 415.0
Overload capacity
*3
(% of rated output
current for 60 sec.)
107 107 108 107 107 120 120 117 117 114 116 120 107 113 120 109 115 120
Current limit (% of
rated output current)
120
Carrier frequency
(kHz)
*5
10 1010 8101515810101010 5 5 8 2 2 2
Maximum output
frequency
400.0Hz
Maximum output voltage
3-phase; 200, 208, 220, 230, or 240Vac
(Proportional to input voltage)
*1 The difference between Heavy Duty ratings and the Normal Duty ratings for the Drive are the rated input and output current, overload capacity, carrier frequency, current limit, and
maximum output frequency. Parameter C6-01 must be set to value of “0” for Heavy Duty ratings and “2” for Normal Duty ratings. Factory default is Heavy Duty (C6-01=0).
*2 Horsepower ratings are based on 230V or 460V NEC Table 430.150. The maximum applicable motor output is given for a standard 4-pole motor. When selecting the actual motor
and Drive, be sure that the Drive's rated output current is appropriate for the motor's rated current.
*3 Models 2110, 4220, 4300 have an overload rating of 120% of rated output current for 60 seconds.
*4 2kHz is the Maximum carrier frequency value and default carrier frequency value for all models.
*5 Each value shown is the Maximum carrier frequency and default carrier frequency.
utput rat
ngs
Heavy Duty
1
Normal Duty
1