GEK-106310AB F650 Digital Bay Controller 5-23
5 SETTINGS 5.3 SYSTEM SETUP
5
• §Underfrequency (81U)
• §Thermal Model (49P)
• §Broken Conductor (I1I2)
• §Load Encroachment
• §Rotor Blocked (48)
• §Setting Groups
• §Recloser (79)
• §Oscillography
• §Synchrocheck (25)
• §Fault Locator
• §Directional Power (32DIR)
• §Overfrequency (81O)
• §Max. number of starts (66)
• §Fuse Failure (VTFF)
• §Watt Gnd Flt Low (32NL)
• §Watt Gnd Flt High (32NH)
• §Data Logger
• §Comparator
• §Switchgear
• §Breaker
When the Out of Service status goes to ON, or the setting has been changed to Enabled, the ready led will also change to
red color. Be careful if ready led is linked to an output, because the output will not change its state. To set an output to ready
state see factory default Logic & Configuration. Take notice that VO_000 is set to the output instead of VO_099
The following figure shows the flow chart of these states

Table of Contents

Other manuals for GE F650

Questions and Answers:

Question and Answer IconNeed help?

Do you have a question about the GE F650 and is the answer not in the manual?

GE F650 Specifications

General IconGeneral
ModelF650
CategoryController
Frequency50/60 Hz
DisplayLCD
TypeFeeder Protection Relay
ApplicationFeeder Protection and Control
Communication ProtocolsDNP3, Modbus, IEC 61850
Protection FunctionsOvercurrent, Earth Fault
ManufacturerGeneral Electric
Input Voltage24-250 VDC/VAC