7-16 F650 Digital Bay Controller GEK-106310AB
7.2 IEC 61850 PROFILE FOR F650 7 IEC 61850 PROTOCOL
7
2.2.2 PICS for T-Profile support
Please refer to the services of Part 7 to see whether these profiles are supported. No distinction is made between A- and T-
Profiles there because the definition only refers to the application.
2.3 MMS conformance
The following conformance statements are conditional upon the support of the client/server A-Profile (e.g. A1 see profile
description in Clause 6) being declared.
Except where present, MMS conformance shall be in accordance with ISO/ISP 14226-2.
2.3.1 MMS Initiate conformance
2.3.1.1 MMS InitiateRequest general parameters
2.3.1.2 MMS InitiateResponse general parameters
A-Profile
shortcut
Profile description
Client Server
Value/comment
realized realized
T1 TCP/IP T-profile N Y
T2 OSI T-profile N N
T3 GOOSE/GSE T-profile Y Y Only GOOSE not GSE
management
T4 GSSE T-profile Y Y
T5 TimeSync T-profile Y N
InitiateRequest
Client-CR Server-CR
realized Value/range realized Value/range
InitiateRequest
localDetailCalling Y
proposedMaxServOutstandingCalling
Y
ProposedMaxServOustandingCalled
Y
InitRequestDetail
Y
InitiateRequestDetail
proposedVersionNumber Y
proposedParameterCBB
Y
servicesSupportedCalling
Y
additionalSupportedCalling
N
additionalCbbSupportedCalling
N
privilegeClassIdentityCalling
N
InitiateRequest
Client-CR Server-CR
realized Value/range realized Value/range
InitiateResponse
localDetailCalled Y
negotiatedMaxServOutstandingCalling
Y1
negotiatedMaxServOustandingCalled
Y3
initResponseDetail
Y
InitiateResponseDetail
Y
negotiatedVersionNumber
Y
negotiatedParameterCBB
Y
servicesSupportedCalled
Y
additionalSupportedCalled
N
additionalCbbSupportedCalled
N
privilegeClassIdentityCalled
N