GEK-106310AB F650 Digital Bay Controller 7-27
7 IEC 61850 PROTOCOL 7.2 IEC 61850 PROFILE FOR F650
7
2.2.1.2 ndPIOC
This logical node class is used for neutral instantaneous overcurrent and has 3 instances inside the device.
Note: ACT includes origin attribute in ST, this is implemented according to Tissue 68.
2.2.1.3 gndPIOC
This logical node class is used for ground instantaneous and sensitive ground instantaneous overcurrent. There are 6
instances of this logical node inside the device.
Note: ACT includes origin attribute in ST, this is implemented according to Tissue 68.
PIOC class
Attribute
Name
Attribute
Type
Explanation M/O/E Notes
PIOC Instantaneous overcurrent
Data
Common Logical Node Information
Mod INC Mode M Status-only
Beh INS Behaviour M
Health INS Health M
NamPlt LPL Name plate M
Status Information
Str ACD Start O IOC PKP
Op ACT Operate M IOC OP
Blk ACT Blk E IOC BLK
Settings
StrVal ASG Start value M Pickup Level (0,05 – 160)
OpDlTmms ING Operate Delay Time E Trip Delay (0-900000)
Units in miliseconds
RsDlTmms ING Reset Delay E Reset Delay (0-900000)
Units in miliseconds
PIOCEna SPG Function IOC enable E Function
PIOC class
Attribute
Name
Attribute
Type
Explanation M/O/E Notes
PIOC Instantaneous overcurrent
Data
Common Logical Node Information
Mod INC Mode M Status-only
Beh INS Behaviour M
Health INS Health M
NamPlt LPL Name plate M
Status Information
Str ACD Start O IOC PKP
Op ACT Operate M IOC OP
Blk ACT Blk E IOC BLK
Settings
StrVal ASG Start value M Pickup Level (0,05 – 160)
OpDlTmms ING Operate Delay Time E Trip Delay (0-900000)
Units in miliseconds
InMagTyp ING Input Type E (Phasor o RMS)
RsDlTmms ING Reset Delay E Reset Delay (0-900000)
Units in miliseconds
PIOCEna SPG Function IOC enable E Function