7-30 F650 Digital Bay Controller GEK-106310AB
7.2 IEC 61850 PROFILE FOR F650 7 IEC 61850 PROTOCOL
7
2.2.4 PTOV (Overvoltage)
2.2.4.1 phsPTOV
This logical node class is used for phase overfvoltage and has 3 instances inside the device.
Note: ACT includes origin attribute in ST, this is implemented according to Tissue 68.
2.2.4.2 auxPTOV
This logical node class is used for auxiliary overfvoltage and has 3 instances inside the device.
Note: ACT includes origin attribute in ST, this is implemented according to Tissue 68.
PTOV class
Attribute
Name
Attribute
Type
Explanation M/O/E Notes
PTOV Overvoltage
Data
Common Logical Node Information
Mod INC Mode M Status-only
Beh INS Behaviour M
Health INS Health M
NamPlt LPL Name plate M
Status Information
Str ACD Start M TOV PKP
Op ACT Operate O TOV OP
Blk ACT Block E TOV BLK
Settings
StrVal ASG Start Value O Pickup Level (3 – 300)
OpDlTmms ING Operate Delay Time O Trip Delay ( 0 – 900000 )
Units in miliseconds
RsDlTmms ING Reset Delay Time O Reset Delay ( 0 – 900000 )
Units in miliseconds
PhLogic ING Logic Mode E Logic ( Any, two, all phases )
PTOVEna SPG Function TOV enable E Function
PTOV class
Attribute
Name
Attribute
Type
Explanation M/O/E Notes
PTOV Overvoltage
Data
Common Logical Node Information
Mod INC Mode M Status-only
Beh INS Behaviour M
Health INS Health M
NamPlt LPL Name plate M
Status Information
Str ACD Start M TOV PKP
Op ACT Operate O TOV OP
Blk ACT Block E TOV BLK
Settings
StrVal ASG Start Value O Pickup Level (3 – 300)
OpDlTmms ING Operate Delay Time O Trip Delay ( 0 – 900000 )
Units in miliseconds
RsDlTmms ING Reset Delay Time O Reset Delay ( 0 – 900000 )
Units in miliseconds
PTOVEna SPG Function TOV enable E Function