GEK-106310AB F650 Digital Bay Controller 7-35
7 IEC 61850 PROTOCOL 7.2 IEC 61850 PROFILE FOR F650
7
2.3.1.2 ndRDIR
This logical node class is used for neutral directional elements and has 3 instances inside the device.
Note: ACT includes origin attribute in ST, this is implemented according to Tissue 68.
2.3.1.3 gndRDIR
This logical node class is used for ground directional elements and has 3 instances inside the device.
Note: ACT includes origin attribute in ST, this is implemented according to Tissue 68.
RDIR class
Attribute
Name
Attribute
Type
Explanation M/O/E Notes
RDIR Directional Element
Data
Common Logical Node Information
Mod INC Mode M Status-only
Beh INS Behaviour M
Health INS Health M
NamPlt LPL Name plate M
Status Information
Dir ACD Direction M Fixed to unknown value
Op ACT Operate E Neutral Dir OP
Blk ACT Block E Neutral Dir Block
BlkIn ACT Neutral Dir Blk Inp E Neutral Dir Blk Inp
Settings
ChrAng ASG Characteristic Angle O (-90, 90) MTA
BlkValV ASG Minimun operating current O (0, 300) Pol V Threshold
PolOpMod ING Direction E (Reverse, Forward)
BlkMod ING Block Logica E (Prmission, Blocked)
RDIREna SPG Function Permission E (Enable, Disable)
PolQty ING Polarisation O (VO,IP,VO+IP,VO*IP)
RDIR class
Attribute
Name
Attribute
Type
Explanation M/O/E Notes
RDIR Directional Element
Data
Common Logical Node Information
Mod INC Mode M Status-only
Beh INS Behaviour M
Health INS Health M
NamPlt LPL Name plate M
Status Information
Dir ACD Direction M Fixed to unknown value
Op ACT Operate E Ground Dir OP
Blk ACT Block E Ground Dir Block
BlkIn ACT Ground Dir Blk Inp E Ground Dir Blk Inp
Settings
ChrAng ASG Characteristic Angle O (-90, 90) MTA
BlkValV ASG Minimun operating current O (0, 300) Pol V Threshold
PolOpMod ING Direction E (Reverse, Forward)
BlkMod ING Block Logical E (Prmission, Blocked)
RDIREna SPG Function Permission E (Enable, Disable)
PolQty ING Polarisation O (VO,IP,VO+IP,VO*IP)