7-34 F650 Digital Bay Controller GEK-106310AB
7.2 IEC 61850 PROFILE FOR F650 7 IEC 61850 PROTOCOL
7
2.3 Logical Nodes for protection related functions. LN Group: R
2.3.1 RDIR (Directional element)
2.3.1.1 phsRDIR
This logical node class is used for phase directional elements and has 3 instances inside the device.
Note: ACT includes origin attribute in ST, this is implemented according to Tissue 68.
RDIR class
Attribute
Name
Attribute
Type
Explanation M/O/E Notes
RDIR Directional Element
Data
Common Logical Node Information
Mod INC Mode M Status-only
Beh INS Behaviour M
Health INS Health M
NamPlt LPL Name plate M
Status Information
Dir ACD Direction M Fixed to unknown value
Op ACT Operate E Phase Dir OP
Blk ACT Block E Phase Dir Block
BlkIn ACT Phase Dir Blk Inp E Phase Dir Blk Inp
Settings
ChrAng ASG Characteristic Angle O (-90, 90) MTA
BlkValV ASG Minimun operating current O (0, 300) Pol V Threshold
PolOpMod ING Direction E (Reverse, Forward)
BlkMod ING Block Logical E (Prmission, Blocked)
RDIREna SPG Function Permission E (Enable, Disable)