GEK-106310AB F650 Digital Bay Controller C-23
APPENDIX C C.8 ANALOG INPUTS
C
The "Fault Type" is represented by enumeration value. The table below shows values with DNP3 setting "Other Scale
Factor = 1".
If the DNP3 setting "Other Scale Factor" has a value different from "1" then "Enum Value" will be scaled by the adjusted
factor. For example if "Other Scale Factor = 0.001", then the value corresponding to "TRIPH" fault type will be 2000.
NAF indicates that the type of fault has not been calculated.
103 Board G - Analog 8
104 Board H - Analog 1
105 Board H - Analog 2
106 Board H - Analog 3
107 Board H - Analog 4
108 Board H - Analog 5
109 Board H - Analog 6
110 Board H - Analog 7
111 Board H - Analog 8
112 Board J - Analog 1
113 Board J - Analog 2
114 Board J - Analog 3
115 Board J - Analog 4
116 Board J - Analog 5
117 Board J - Analog 6
118 Board J - Analog 7
119 Board J - Analog 8
ENUM VALUE FAULT TYPE
0 GROUND
1 PHASE
2TRIPH
3AG
4 ABG
5AB
6BG
7BCG
8BC
9CG
10 CAG
11 CA
12 NAF