Return to Table of Contents Troubleshooting Guide - Electrical System Page 4-1
4.0 Troubleshooting Guide Electrical System
PROBLEM
CAUSE
SOLUTION
Compressor is not
running.
No power to condensing unit.
Check condensing unit is plugged in.
Check power at internal receptacle.
No call for cooling from control.
Check control settings or for bad control.
Incorrectly wired connections in
condensing unit.
Verify wiring per wiring diagram, Section
7.2. Reconnect wires if needed.
Incorrect control settings.
Return to factory settings.
See Sections 7.5.1 and 7.5.2.
No power to compressor.
Restore power to unit.
Refer to information plate. See Section
1.2 and Table 7-1
Faulty control.
Refer to Control not functioning.
Starting device is not operational (start
relay/capacitor).
Replace compressor electrical
components.
Faulty compressor.
Replace compressor per Section 6.14.
Condenser fan is not
running.
No power to fan
Restore power to unit.
Refer to information plate. See Section
1.0 and Table 7-1
Incorrectly wired harness.
Verify wiring per wiring diagram, Section
7.2. Reconnect wires if needed.
Fan is obstructed.
Remove obstructions.
Fan still does not run.
Replace condenser fan per Section 6.13.
Evaporator fan is not
running.
No power to evaporator fan motor.
Restore power to unit.
Refer to information plate. See Section
1.0 and Table 7-1
Fan is obstructed.
Remove obstruction.
Incorrectly wired harness.
Verify wiring per wiring diagram, Section
7.2. Reconnect wires if needed.
If Evaporator fan is still not running…
Replace evaporator fan per Section 6.13.
BBSLP series ONLY: No power to/from
DC inverter/driver (12V).
If no power: restore power, replace. Refer
to Section 1.1.