EasyManuals Logo

GE F60 User Manual

GE F60
732 pages
To Next Page IconTo Next Page
To Next Page IconTo Next Page
To Previous Page IconTo Previous Page
To Previous Page IconTo Previous Page
Page #162 background imageLoading...
Page #162 background image
5-30 F60 Feeder Protection System GE Multilin
5.2 PRODUCT SETUP 5 SETTINGS
5
d) NETWORK
As outlined in the previous section, when using more than one Ethernet port, configure each to belong to a different net-
work or subnet using the IP addresses and mask. Configure the network IP and subnet settings before configuring the rout-
ing settings.
To obtain a list of all port numbers used, for example for audit purposes, contact GE technical support with substantiating
information, such as the serial number and order code of your device.
PATH: SETTINGS PRODUCT SETUP  COMMUNICATIONS  NETWORK 1(3)
The IP addresses are used with the DNP, Modbus/TCP, IEC 61580, IEC 60870-5-104, TFTP, HTTP, and PRP protocols.
PRP is explained in its own section later.
PRT1 (2 OR 3) IP ADDRESS: This setting sets the ports IPv4 address in standard IPV4 format. This setting is valid on port 3 if
port 2
REDUNDANCY is set to None.
PRT1 (2 OR 3) SUBNET MASK: This setting sets the ports IPv4 subnet mask in standard IPV4 format. This setting is valid on
port 3 if port 2
REDUNDANCY is set to None.
PRT1 (2 OR 3) GOOSE ENABLED: This setting enables/disables Goose on the respective port. By default Goose is enabled.
PRT2 REDUNDANCY determines if ports 2 and 3 operate in redundant or independent mode. If a license for PRP was pur-
chased, the options are None, Failover, and PRP. If a license for PRP was not purchased, the available options are None
and Failover. In non-redundant mode (
REDUNDANCY set to None), ports 2 and 3 operate independently with their own MAC,
IP, and mask addresses. If REDUNDANCY is set to Failover, the operation of ports 2 and 3 is as follows:
Ports 2 and 3 use the port 2 MAC address, IP address, and mask
The configuration fields for IP address and mask on port 3 are hidden
NETWORK PORT 1
PRT1 IP ADDRESS:
127.0.0.1
Range: Standard IPV4 address format
MESSAGE
PRT1 SUBNET IP MASK:
255.0.0.0
Range: Standard IPV4 address format
MESSAGE
PRT1 GOOSE ENABLED:
Enabled
Range: Enabled, Disabled
NETWORK PORT 2
PRT2 IP ADDRESS:
127.0.0.1
Range: Standard IPV4 address format
MESSAGE
PRT2 SUBNET IP MASK:
255.0.0.0
Range: Standard IPV4 address format
MESSAGE
PRT2 REDUNDANCY:
None
Range: None, Failover, PRP
None, Failover (if no PRP license)
MESSAGE
PRT2 PRP MCST ADDR:
01-15-4E-00-01-00
Range: 01-15-4E-00-01-00 to 01-15-4E-00-01-FF
MESSAGE
PRT2 GOOSE ENABLED:
Enabled
Range: Enabled, Disabled
NETWORK PORT 3
PRT3 IP ADDRESS:
127.0.0.1
Range: Standard IPV4 address format
MESSAGE
PRT3 SUBNET IP MASK:
255.0.0.0
Range: Standard IPV4 address format
MESSAGE
PRT3 GOOSE ENABLED:
Enabled
Range: Enabled, Disabled

Table of Contents

Questions and Answers:

Question and Answer IconNeed help?

Do you have a question about the GE F60 and is the answer not in the manual?

GE F60 Specifications

General IconGeneral
Frequency50/60 Hz
ManufacturerGE (General Electric)
Communication ProtocolsDNP3, IEC 61850
MountingPanel Mount
DisplayLCD
Power Supply24-250V DC
Current Rating5A
StandardsIEC 60255
Device TypeProtection Relay
Protection FunctionsOvercurrent