GE Multilin F60 Feeder Protection System 5-115
5 SETTINGS 5.4 SYSTEM SETUP
5
The switch element has direct hard-coded connections to IEC 61850 model as shown in the logic diagram. This allows
remote open/close operation of each switch, using either CSWI or XSWI IEC 61850 logical nodes. IEC 61850 select-
before-operate functionality, local/remote switch functionality along with a blocking open/close commands are provided.
Note that IEC 61850 commands are event-driven and dwell time for these is one protection pass only. If you want to main-
tain close/open command for a certain time, do so either on the contact outputs using the "Seal-in" setting or in FlexLogic.
5.4.6 FLEXCURVES
a) SETTINGS
PATH: SETTINGS  SYSTEM SETUP  FLEXCURVES FLEXCURVE A(D)
FlexCurves A through D have settings for entering times to reset and operate at the following pickup levels: 0.00 to 0.98
and 1.03 to 20.00. This data is converted into two continuous curves by linear interpolation between data points. To enter a
custom FlexCurve, enter the reset and operate times (using the VALUE keys) for each selected pickup point (using the
MESSAGE UP/DOWN keys) for the desired protection curve (A, B, C, or D).
FLEXCURVE A
FLEXCURVE A TIME AT
0.00 xPKP: 0 ms
Range: 0 to 65535 ms in steps of 1
Table 5–13: FLEXCURVE TABLE
RESET TIME
MS
RESET TIME
MS
OPERATE TIME
MS
OPERATE TIME
MS
OPERATE TIME
MS
OPERATE TIME
MS
0.00 0.68 1.03 2.9 4.9 10.5
0.05 0.70 1.05 3.0 5.0 11.0
0.10 0.72 1.1 3.1 5.1 11.5
0.15 0.74 1.2 3.2 5.2 12.0
0.20 0.76 1.3 3.3 5.3 12.5
0.25 0.78 1.4 3.4 5.4 13.0
0.30 0.80 1.5 3.5 5.5 13.5
0.35 0.82 1.6 3.6 5.6 14.0
0.40 0.84 1.7 3.7 5.7 14.5
0.45 0.86 1.8 3.8 5.8 15.0
0.48 0.88 1.9 3.9 5.9 15.5
0.50 0.90 2.0 4.0 6.0 16.0
0.52 0.91 2.1 4.1 6.5 16.5
0.54 0.92 2.2 4.2 7.0 17.0
0.56 0.93 2.3 4.3 7.5 17.5
0.58 0.94 2.4 4.4 8.0 18.0
0.60 0.95 2.5 4.5 8.5 18.5
0.62 0.96 2.6 4.6 9.0 19.0
0.64 0.97 2.7 4.7 9.5 19.5
0.66 0.98 2.8 4.8 10.0 20.0

Table of Contents

Questions and Answers:

Question and Answer IconNeed help?

Do you have a question about the GE F60 and is the answer not in the manual?

GE F60 Specifications

General IconGeneral
Frequency50/60 Hz
ManufacturerGE (General Electric)
Communication ProtocolsDNP3, IEC 61850
MountingPanel Mount
DisplayLCD
Power Supply24-250V DC
Current Rating5A
StandardsIEC 60255
Device TypeProtection Relay
Protection FunctionsOvercurrent

Related product manuals