2-22 F60 Feeder Protection System GE Multilin
2.4 SPECIFICATIONS 2 PRODUCT DESCRIPTION
2
BREAKER FLASHOVER
Operating quantity: phase current, voltage and voltage differ-
ence
Pickup level voltage: 0 to 1.500 pu in steps of 0.001
Dropout level voltage: 97 to 98% of pickup
Pickup level current: 0 to 1.500 pu in steps of 0.001
Dropout level current: 97 to 98% of pickup
Level accuracy: ±0.5% or ±0.1% of rated, whichever is
greater
Pickup delay: 0 to 65.535 s in steps of 0.001
Timer accuracy: ±3% of operate time or ±42 ms, which-
ever is greater
Operate time: <42 ms at 1.10 × pickup at 60 Hz
BREAKER RESTRIKE
Principle: detection of high-frequency overcurrent
condition ¼ cycle after breaker opens
Availability: one per CT/VT module (not including 8Z
modules)
Pickup level: 0.1 to 2.00 pu in steps of 0.01
Reset delay: 0.000 to 65.535 s in steps of 0.001
INCIPIENT CABLE FAULT DETECTION
Principle: detection of ½ cycle or less overcurrent
condition during normal load
Availability: two per CT/VT module (not including 8Z
modules)
Pickup level: 0.1 to 10.00 pu in steps of 0.01
Reset delay: 0.000 to 65.535 s in steps of 0.001
Operating mode: number of counts, counts per time win-
dow
SYNCHROCHECK
Max voltage difference: 0 to 400000 V in steps of 1
Max angle difference: 0 to 100
° in steps of 1
Max freq. difference: 0.00 to 2.00 Hz in steps of 0.01
Hysteresis for max. freq. diff.: 0.00 to 0.10 Hz in steps of 0.01
Dead source function: None, LV1 & DV2, DV1 & LV2, DV1 or
DV2, DV1 xor DV2, DV1 & DV2
(L = Live, D = Dead)
AUTORECLOSURE
Single breaker applications, 3-pole tripping schemes
Up to 4 reclose attempts before lockout
Independent dead time setting before each shot
Possibility of changing protection settings after each shot with
FlexLogic
LOAD ENCROACHMENT
Responds to: Positive-sequence quantities
Minimum voltage: 0.000 to 3.000 pu in steps of 0.001
Reach (sec. Ω): 0.02 to 250.00 Ω in steps of 0.01
Impedance accuracy: ±5%
Angle: 5 to 50° in steps of 1
Angle accuracy: ±2°
Pickup delay: 0 to 65.535 s in steps of 0.001
Reset delay: 0 to 65.535 s in steps of 0.001
Timer accuracy: ±3% of operate time or ±1/4 cycle
(whichever is greater)
Operate time: <30 ms at 60 Hz
THERMAL OVERLOAD PROTECTION
Thermal overload curves: IEC 255-8 curve
Base current: 0.20 to 3.00 pu in steps of 0.01
Overload (k) factor: 1.00 to 1.20 pu in steps of 0.05
Trip time constant: 0 to 1000 min. in steps of 1
Reset time constant: 0 to 1000 min. in steps of 1
Minimum reset time: 0 to 1000 min. in steps of 1
Timer accuracy (cold curve): ±100 ms or 2%, whichever is greater
Timer accuracy (hot curve): ±500 ms or 2%, whichever is greater
for I
p
< 0.9 × k × I
b
and I / (k × I
b
) > 1.1
TRIP BUS (TRIP WITHOUT FLEXLOGIC)
Number of elements: 6
Number of inputs: 16
Operate time: <2 ms at 60 Hz
Timer accuracy: ±3% or 10 ms, whichever is greater
2.4.2 USER-PROGRAMMABLE ELEMENTS
FLEXLOGIC
Programming language: Reverse Polish Notation with graphical
visualization (keypad programmable)
Lines of code: 512
Internal variables: 64
Supported operations: NOT, XOR, OR (2 to 16 inputs), AND (2
to 16 inputs), NOR (2 to 16 inputs),
NAND (2 to 16 inputs), latch (reset-domi-
nant), edge detectors, timers
Inputs: any logical variable, contact, or virtual
input
Number of timers: 32
Pickup delay: 0 to 60000 (ms, sec., min.) in steps of 1
Dropout delay: 0 to 60000 (ms, sec., min.) in steps of 1
FLEXCURVES™
Number: 4 (A through D)
Reset points: 40 (0 through 1 of pickup)
Operate points: 80 (1 through 20 of pickup)
Time delay: 0 to 65535 ms in steps of 1
FLEX STATES
Number: up to 256 logical variables grouped
under 16 Modbus addresses
Programmability: any logical variable, contact, or virtual
input