5-182 F60 Feeder Protection System GE Multilin
5.6 GROUPED ELEMENTS 5 SETTINGS
5
The phase directional element responds to the forward load current. In the case of a following reverse fault, the ele-
ment needs some time – in the order of 8 ms – to establish a blocking signal. Some protection elements such as
instantaneous overcurrent may respond to reverse faults before the blocking signal is established. Therefore, a
coordination time of at least 10 ms must be added to all the instantaneous protection elements under the supervi-
sion of the phase directional element. If current reversal is of a concern, a longer delay – in the order of 20 ms –
may be needed.
Figure 5–73: PHASE DIRECTIONAL SCHEME LOGIC
5.6.5 NEUTRAL CURRENT
a) MAIN MENU
PATH: SETTINGS  GROUPED ELEMENTS SETTING GROUP 1(6)  NEUTRAL CURRENT
NEUTRAL CURRENT
NEUTRAL TOC1
See page 5–183.
MESSAGE
NEUTRAL TOC2
See page 5–183.
MESSAGE
NEUTRAL TOC3
See page 5–183.
MESSAGE
NEUTRAL TOC4
See page 5–183.
MESSAGE
NEUTRAL IOC1
See page 5–184.
NOTE
FLEXLOGIC OPERAND
FLEXLOGIC OPERAND
FLEXLOGIC OPERAND
FLEXLOGIC OPERAND
SETTING
SETTING
SETTING
SETTING
SETTING
SETTING
PHASE DIR 1
FUNCTION:
PHASE DIR 1 SOURCE:
PHASE DIR 1 BLOCK OC
WHEN V MEM EXP:
PHASE DIR 1
BLOCK:
PHASE DIR 1 ECA:
PHASE DIR 1 POL V
THRESHOLD:
PH DIR1 BLK A
PH DIR1 BLK B
PH DIR1 BLK C
PH DIR1 BLK
IA
No
Seq=ABC Seq=ACB
Yes
VBC VCB
827078A7.CDR
Off=0
V MINIMUM
-Use V when V Min
-Use V memory when
V < Min
I 0.05 pu
Enabled=1
AND
AND
OR
MEMORY TIMER
1 cycle
1 sec
Vpol
0
I
1
RUN
AND
PHASE B LOGIC SIMILAR TO PHASE A
PHASE C LOGIC SIMILAR TO PHASE A
OR
USE ACTUAL VOLTAGE
USE MEMORIZED VOLTAGE

Table of Contents

Questions and Answers:

Question and Answer IconNeed help?

Do you have a question about the GE F60 and is the answer not in the manual?

GE F60 Specifications

General IconGeneral
Frequency50/60 Hz
ManufacturerGE (General Electric)
Communication ProtocolsDNP3, IEC 61850
MountingPanel Mount
DisplayLCD
Power Supply24-250V DC
Current Rating5A
StandardsIEC 60255
Device TypeProtection Relay
Protection FunctionsOvercurrent

Related product manuals