GE Multilin F60 Feeder Protection System 6-27
6 ACTUAL VALUES 6.3 METERING
6
6.3.13 TRANSDUCER INPUTS AND OUTPUTS
PATH: ACTUAL VALUES  METERING  TRANSDUCER I/O DCMA INPUTS DCMA INPUT xx
Actual values for each dcmA input channel that is enabled are displayed with the top line as the programmed channel ID
and the bottom line as the value followed by the programmed units.
PATH: ACTUAL VALUES  METERING  TRANSDUCER I/O RTD INPUTS RTD INPUT xx
Actual values for each RTD input channel that is enabled are displayed with the top line as the programmed channel ID and
the bottom line as the value.
DCMA INPUT xx
DCMA INPUT xx
0.000 mA
RTD INPUT xx
RTD INPUT xx
-50 °C