GE Multilin F60 Feeder Protection System 2-11
2 PRODUCT DESCRIPTION 2.2 ORDER CODES
2
2.2.3 ORDER CODES WITH PROCESS BUS MODULES
The order codes for the horizontal mount units with the process bus module are shown below.
POWER SUPPLY H | | | | 125 / 250 V AC/DC power supply
L | | | | 24 to 48 V (DC only) power supply
ENHANCED DIAGNOSTICS CT/VT DSP
(8L, 8M, 8N, 8R require DSP to be enhanced diagnostic)
XX | XX | No DSP module (slots M and U only)
8L | 8L | Standard 4CT/4VT with enhanced diagnostics
8M | 8M | Sensitive Ground 4CT/4VT with enhanced diagnostics
8N | 8N | Standard 8CT with enhanced diagnostics
8R | 8R | Sensitive Ground 8CT with enhanced diagnostics
| | 8Z * | Hi-Z 4CT (required for high-impedance fault detection element)
DIGITAL INPUTS/OUTPUTS XX XX XX No Module
4A 4A 4A 4 Solid-State (no monitoring) MOSFET outputs
4B 4B 4B 4 Solid-State (voltage with optional current) MOSFET outputs
4C 4C 4C 4 Solid-State (current with optional voltage) MOSFET outputs
4D 4D 4D 16 digital inputs with Auto-Burnishing (maximum of three modules within a case)
4L 4L 4L 14 Form-A (no monitoring) Latching outputs
67 67 67 8 Form-A (no monitoring) outputs
6A 6A 6A 2 Form-A (voltage with optional current) and 2 Form-C outputs, 8 digital inputs
6B 6B 6B 2 Form-A (voltage with optional current) and 4 Form-C outputs, 4 digital inputs
6C 6C 6C 8 Form-C outputs
6D 6D 6D 16 digital inputs
6E 6E 6E 4 Form-C outputs, 8 digital inputs
6F 6F 6F 8 Fast Form-C outputs
6G 6G 6G 4 Form-A (voltage with optional current) outputs, 8 digital inputs
6H 6H 6H 6 Form-A (voltage with optional current) outputs, 4 digital inputs
6K 6K 6K 4 Form-C and 4 Fast Form-C outputs
6L 6L 6L 2 Form-A (current with optional voltage) and 2 Form-C outputs, 8 digital inputs
6M 6M 6M 2 Form-A (current with optional voltage) and 4 Form-C outputs, 4 digital inputs
6N 6N 6N 4 Form-A (current with optional voltage) outputs, 8 digital inputs
6P 6P 6P 6 Form-A (current with optional voltage) outputs, 4 digital inputs
6R 6R 6R 2 Form-A (no monitoring) and 2 Form-C outputs, 8 digital inputs
6S 6S 6S 2 Form-A (no monitoring) and 4 Form-C outputs, 4 digital inputs
6T 6T 6T 4 Form-A (no monitoring) outputs, 8 digital inputs
6U 6U 6U 6 Form-A (no monitoring) outputs, 4 digital inputs
6V 6V 6V 2 Form-A outputs, 1 Form-C output, 2 Form-A (no monitoring) latching outputs, 8 digital inputs
TRANSDUCER
INPUTS/OUTPUTS
(select a maximum of 3 per unit)
5A 5A 5A 4 DCmA inputs, 4 DCmA outputs (only one 5A module is allowed)
5C 5C 5C 8 RTD inputs
5D 5D 5D 4 RTD inputs, 4 DCmA outputs (only one 5D module is allowed)
5E 5E 5E 4 RTD inputs, 4 DCmA inputs
5F 5F 5F 8 DCmA inputs
INTER-RELAY
COMMUNICATIONS
(select a maximum of 1 per unit)
For the last module, slot P is used for digital and transducer
input/output modules; slot R is used for inter-relay
communications modules.
2A C37.94SM, 1300 nm single-mode, ELED, 1 channel single-mode
2B C37.94SM, 1300 nm single-mode, ELED, 2 channel single-mode
2E Bi-phase, single channel
2F Bi-phase, dual channel
2G IEEE C37.94, 820 nm, 128 kbps, multimode, LED, 1 Channel
2H IEEE C37.94, 820 nm, 128 kbps, multimode, LED, 2 Channels
2I Channel 1 - IEEE C37.94, MM, 64/128 kbps; Channel 2 - 1300 nm, single-mode, Laser
2J Channel 1 - IEEE C37.94, MM, 64/128 kbps; Channel 2 - 1550 nm, single-mode, Laser
72 1550 nm, single-mode, Laser, 1 Channel
73 1550 nm, single-mode, Laser, 2 Channel
74 Channel 1 - RS422; Channel 2 - 1550 nm, single-mode, Laser
75 Channel 1 - G.703; Channel 2 - 1550 nm, single-mode Laser
76 IEEE C37.94, 820 nm, 64 kbps, multimode, LED, 1 Channel
77 IEEE C37.94, 820 nm, 64 kbps, multimode, LED, 2 Channels
7A 820 nm, multimode, LED, 1 Channel
7B 1300 nm, multimode, LED, 1 Channel
7C 1300 nm, single-mode, ELED, 1 Channel
7D 1300 nm, single-mode, Laser, 1 Channel
7E Channel 1 - G.703; Channel 2 - 820 nm, multimode
7F Channel 1 - G.703; Channel 2 - 1300 nm, multimode
7G Channel 1 - G.703; Channel 2 - 1300 nm, single-mode ELED
7H 820 nm, multimode, LED, 2 Channels
7I 1300 nm, multimode, LED, 2 Channels
7J 1300 nm, single-mode, ELED, 2 Channels
7K 1300 nm, single-mode, Laser, 2 Channels
7L Channel 1 - RS422; Channel 2 - 820 nm, multimode, LED
7M Channel 1 - RS422; Channel 2 - 1300 nm, multimode, LED
7N Channel 1 - RS422; Channel 2 - 1300 nm, single-mode, ELED
7P Channel 1 - RS422; Channel 2 - 1300 nm, single-mode, Laser
7Q Channel 1 - G.703; Channel 2 - 1300 nm, single-mode Laser
7R G.703, 1 Channel
7S G.703, 2 Channels
7T RS422, 1 Channel
7W RS422, 2 Channels
* When an 8Z module is ordered, slot F must have an 8F or 8G module.
Table 2–6: F60 ORDER CODES (HORIZONTAL UNITS WITH PROCESS BUS)
F60 - * ** - * * * - F ** - H ** - M ** - P ** - U ** - W/X ** Full Size Horizontal Mount
BASE UNIT F60 | | | | | | | | | | | Base Unit
CPU T | | | | | | | | | | RS485 and Three Multi-mode fiber 100Base-FX (SFP with LC)
U | | | | | | | | | | RS485 and Two Multi-mode fiber 100Base-FX (SFP with LC), One 10/100Base-T (SFP with RJ45)
V | | | | | | | | | | RS485 and Three 10/100Base-T (SFP with RJ45)
SOFTWARE 00 | | | | | | | | | No Software Options
01 | | | | | | | | | Ethernet Global Data (EGD)
03 | | | | | | | | | IEC 61850
04 | | | | | | | | | Ethernet Global Data (EGD) and IEC 61850
06 | | | | | | | | | Phasor measurement unit (PMU)
07 | | | | | | | | | Phasor measurement unit (PMU) and IEC 61850
A0 | | | | | | | | | CyberSentry Lvl 1
A1 | | | | | | | | | CyberSentry Lvl 1 and Ethernet Global Data (EGD)
A3 | | | | | | | | | CyberSentry Lvl 1 and IEC 61850
A4 | | | | | | | | | CyberSentry Lvl 1 and IEC 61850 and Ethernet Global Data (EGD)
A6 | | | | | | | | | CyberSentry Lvl 1 and phasor measurment unit (PMU)
A7 | | | | | | | | | CyberSentry Lvl 1 and IEC 61850 and phasor measurement unit (PMU)
B0 | | | | | | | | | IEEE 1588
B1 | | | | | | | | | IEEE 1588 and Ethernet Global Data (EGD)
B3 | | | | | | | | | IEEE 1588 and IEC 61850
B4 | | | | | | | | | IEEE 1588 and IEC 61850 and Ethernet Global Data (EGD)
B6 | | | | | | | | | IEEE 1588 and phasor measurement unit (PMU)
B7 | | | | | | | | | IEEE 1588 and IEC 61850 and phasor measurement unit (PMU)
C0 | | | | | | | | | Parallel Redundancy Protocol (PRP)
C1 | | | | | | | | | PRP and Ethernet Global Data
C3 | | | | | | | | | PRP and IEC 61850
C4 | | | | | | | | | PRP, Ethernet Global Data, and IEC 61850
C6 | | | | | | | | | PRP and PMU
C7 | | | | | | | | | PRP, IEC 61850, and PMU
D0 | | | | | | | | | IEEE 1588 and CyberSentry Lvl 1
D1 | | | | | | | | | IEEE 1588 and CyberSentry Lvl 1 and Ethernet Global Data (EGD)
D3 | | | | | | | | | IEEE 1588 and CyberSentry Lvl 1 and IEC 61850
D4 | | | | | | | | | IEEE 1588 and CyberSentry Lvl 1 and IEC 61850 and Ethernet Global Data (EGD)
D6 | | | | | | | | | IEEE 1588 and CyberSentry Lvl 1 and phasor measurement unit (PMU)
D7 | | | | | | | | | IEEE 1588 and CyberSentry Lvl 1 and IEC 61850 and phasor measurement unit (PMU)
E0 | | | | | | | | | IEEE 1588 and PRP
E1 | | | | | | | | | IEEE 1588, PRP, and Ethernet Global Dada
Table 2–5: F60 ORDER CODES (REDUCED SIZE VERTICAL UNITS)
F60 - * ** - * * * - F ** - H ** - M ** - P/R ** Reduced Size Vertical Mount (see note regarding P/R slot below)

Table of Contents

Questions and Answers:

Question and Answer IconNeed help?

Do you have a question about the GE F60 and is the answer not in the manual?

GE F60 Specifications

General IconGeneral
Frequency50/60 Hz
ManufacturerGE (General Electric)
Communication ProtocolsDNP3, IEC 61850
MountingPanel Mount
DisplayLCD
Power Supply24-250V DC
Current Rating5A
StandardsIEC 60255
Device TypeProtection Relay
Protection FunctionsOvercurrent