6-12 F60 Feeder Protection System GE Multilin
6.2 STATUS 6 ACTUAL VALUES
6
6.2.21 INCIPIENT FAULT DETECTOR
PATH: ACTUAL VALUES STATUS  INCIPIENT FAULT INCIPIENT FAULT 1(2)
The number of detected incipient faults for each incipient fault element are displayed here for each phase. These values
can be reset to zero with the
COMMANDS  CLEAR RECORDS  CLEAR INCIPENT FAULT COUNTERS command.
6.2.22 REMAINING CONNECTION STATUS
PATH: ACTUAL VALUES STATUS  COMM STATUS REMAINING CONNECT
These values specify the remaining number of TCP connections still available for each protocol. The display depends on
the options applicable to your device, for example the PMU entry does not display when not applicable. Each time a con-
nection is used, the remaining number of connections decrements. When released, the remaining number of connections
increments. If no connection is made over the specific protocol, the number equals the maximum number available for the
specific protocol.
For example, the maximum number of Modbus TCP connections is 4. Once an EnerVista session is opened on a computer
connected to the UR over Ethernet, the Modbus TCP status shows 3. If the EnerVista application is closed, the Modbus
TCP status shows 4.
MMS TCP — The number of IEC 61850 connections remaining.
PMU TCP — The maximum number of PMU TCP connections matches the number of aggregators. The maximum number
of aggregators for the N60 is 4. The maximum number for the C60 is 2. The maximum number is 1 for other products with
a PMU. The remaining number of aggregators displays here.
6.2.23 PARALLEL REDUNDANCY PROTOCOL (PRP)
The Parallel Redundancy Protocol (PRP) defines a redundancy protocol for high availability in substation automation net-
works.
INCIPIENT FAULT 1
INCIPIENT FAULT 1
PH A FAULTS: 0
Range: 0 to 65535 in steps of 1
MESSAGE
INCIPIENT FAULT 1
PH B FAULTS: 0
Range: 0 to 65535 in steps of 1
MESSAGE
INCIPIENT FAULT 1
PH C FAULTS: 0
Range: 0 to 65535 in steps of 1
COMM STATUS
REMAINING CONNECT
MMS TCP(max 5)
5
Range: 0 to 5
MESSAGE
MODBUS TCP(max 4)
4
Range: 0 to 4
MESSAGE
DNP TCP (max 2)
2
Range: 0 to 2
MESSAGE
IEC-104 (max 2)
2
Range: 0 to 2
MESSAGE
PMU TCP
1
Range: 1 to 4

Table of Contents