GE Multilin F60 Feeder Protection System 5-183
5 SETTINGS 5.6 GROUPED ELEMENTS
5
b) NEUTRAL TIME OVERCURRENT (ANSI 51N, IEC PTOC)
PATH: SETTINGS  GROUPED ELEMENTS SETTING GROUP 1(6)  NEUTRAL CURRENT NEUTRAL TOC1(4)
The neutral time overcurrent element can provide a desired time-delay operating characteristic versus the applied current
or be used as a simple definite time element. The neutral current input value is a quantity calculated as 3Io from the phase
currents and may be programmed as fundamental phasor magnitude or total waveform RMS magnitude as required by the
application.
MESSAGE
NEUTRAL IOC8
See page 5–184.
MESSAGE
NEUTRAL
DIRECTIONAL OC1
See page 5–185.
MESSAGE
NEUTRAL
DIRECTIONAL OC2
See page 5–185.
NEUTRAL TOC1
NEUTRAL TOC1
FUNCTION: Disabled
Range: Disabled, Enabled
MESSAGE
NEUTRAL TOC1 SIGNAL
SOURCE: SRC 1
Range: SRC 1, SRC 2, SRC 3, SRC 4
MESSAGE
NEUTRAL TOC1
INPUT: Phasor
Range: Phasor, RMS
MESSAGE
NEUTRAL TOC1
PICKUP: 1.000 pu
Range: 0.000 to 30.000 pu in steps of 0.001
MESSAGE
NEUTRAL TOC1
CURVE: IEEE Mod Inv
Range: See OVERCURRENT CURVE TYPES table
MESSAGE
NEUTRAL TOC1
TD MULTIPLIER: 1.00
Range: 0.00 to 600.00 in steps of 0.01
MESSAGE
NEUTRAL TOC1
RESET: Instantaneous
Range: Instantaneous, Timed
MESSAGE
NEUTRAL TOC1 BLOCK:
Off
Range: FlexLogic operand
MESSAGE
NEUTRAL TOC1
TARGET: Self-reset
Range: Self-reset, Latched, Disabled
MESSAGE
NEUTRAL TOC1
EVENTS: Disabled
Range: Disabled, Enabled

Table of Contents

Questions and Answers:

Question and Answer IconNeed help?

Do you have a question about the GE F60 and is the answer not in the manual?

GE F60 Specifications

General IconGeneral
Frequency50/60 Hz
ManufacturerGE (General Electric)
Communication ProtocolsDNP3, IEC 61850
MountingPanel Mount
DisplayLCD
Power Supply24-250V DC
Current Rating5A
StandardsIEC 60255
Device TypeProtection Relay
Protection FunctionsOvercurrent

Related product manuals