5-82 F60 Feeder Protection System GE Multilin
5.2 PRODUCT SETUP 5 SETTINGS
5
An event is logged in the event record (as per user setting) when a control pushbutton is pressed. No event is logged when
the pushbutton is released. The faceplate keys (including control keys) cannot be operated simultaneously – a given key
must be released before the next one can be pressed.
The control pushbuttons become user-programmable only if the breaker control feature is not configured for manual control
via the USER 1 through 3 pushbuttons as shown below. If configured for manual control, breaker control typically uses the
larger, optional user-programmable pushbuttons, making the control pushbuttons available for other user applications.
Figure 5–13: CONTROL PUSHBUTTON LOGIC
842010A2.CDR
CONTROL PUSHBUTTON
1 FUNCTION:
SYSTEM SETUP/
BREAKERS/BREAKER 1/
BREAKER 1 PUSHBUTTON
:CONTROL
SYSTEM SETUP/
BREAKERS/BREAKER 2/
BREAKER 2 PUSHBUTTON
:CONTROL
SETTING
SETTINGS
TIMER
FLEXLOGIC OPERAND
Enabled=1
Enabled=1
When applicable
Enabled=1
RUN
OFF
ON
AND
100 msec
0
CONTROL PUSHBTN 1 ON
{

Table of Contents