Description of problem: The number of failures threshold was exceeded.
What to do: Wait for the lockout interval and try to authenticate again.
Message: "Unauthorized firmware attempt"
Latched target message: No.
Description of problem: A firmware upgrade operation was attempted while the lock relay setting was enabled.
What to do: Ask the Supervisor to unlock the relay and try again.
Message: "Unauthorized setting write"
Latched target message: No.
Description of problem: A setting write was attempted while the lock relay setting was enabled.
What to do: Ask the Supervisor to unlock the settings and try again.
Message: "An attempt to contact the Radius server has failed"
Latched target message: No.
Description of problem: The RADIUS authentication server is unavailable.
What to do: Verify network connectivity and try again.
d) WRONG TRANSCEIVER MESSAGES
Description: The type of SFP does not match the CPU type.
T-type CPU = All ports support fiber SFPs only
Type: minor
Target: latched
Message: "WRONG TRANSCEIVER"
A webpage "SFP Transceiver Information" is provided. This page displays the type of the SFP in it. This data is to be used
with the CPU type to know the cause of the problem.
e) SFP X MODULE FAIL MESSAGES
Description: A faulty SFP or unplugging the SFP would generate this self test.
Type: minor
Target: self reset
Message: SFP MODULE x FAIL
The webpage "SFP Transceiver Information" described in the previous section applies for this self test as well. The "SFP
Module Fail" has higher priority and it suppresses the "Ethernet Fail" target message. The "SFP MODULE FAIL FUNC-
TION" setting enables/disables this self test. The target for this self test is priority-based, with the third one being the high-
est priority. For example, if all three SFP modules fail, then the third SFP target is activated. If the third SFP module failure
resolves, then the second SFP target is activated.