2-20 F60 Feeder Protection System GE Multilin
2.4 SPECIFICATIONS 2 PRODUCT DESCRIPTION
2
PHASE DIRECTIONAL OVERCURRENT
Relay connection: 90° (quadrature)
Quadrature voltage: ABC phase seq.: phase A (V
BC
), phase
B (V
CA
), phase C (V
AB
); ACB phase
seq.: phase A (V
CB
), phase B (V
AC
),
phase C (V
BA
)
Polarizing voltage threshold: 0.000 to 3.000 pu in steps of 0.001
Current sensitivity threshold: 0.05 pu
Characteristic angle: 0 to 359
° in steps of 1
Angle accuracy: ±2°
Operation time (FlexLogic operands):
Tripping (reverse load, forward fault):<
12 ms, typically
Blocking (forward load, reverse fault):<
8 ms, typically
NEUTRAL DIRECTIONAL OVERCURRENT
Directionality: Co-existing forward and reverse
Polarizing: Voltage, Current, Dual, Dual-V, Dual-I
Polarizing voltage: V_0 or VX
Polarizing current: IG
Operating current: I_0
Level sensing: 3 × (|I_0| – K × |I_1|), IG
Restraint, K: 0.000 to 0.500 in steps of 0.001
Characteristic angle: –90 to 90° in steps of 1
Limit angle: 40 to 90° in steps of 1, independent for
forward and reverse
Angle accuracy: ±2°
Offset impedance: 0.00 to 250.00 Ω in steps of 0.01
Pickup level: 0.002 to 30.000 pu in steps of 0.01
Dropout level: 97 to 98%
Operation time: <16 ms at 3 × pickup at 60 Hz
NEGATIVE SEQUENCE DIRECTIONAL OC
Directionality: Co-existing forward and reverse
Polarizing: Voltage
Polarizing voltage: V_2
Operating current: I_2
Level sensing:
Zero-sequence:|I_0| – K × |I_1|
Negative-sequence:|I_2| – K × |I_1|
Restraint, K: 0.000 to 0.500 in steps of 0.001
Characteristic angle: 0 to 90° in steps of 1
Limit angle: 40 to 90° in steps of 1, independent for
forward and reverse
Angle accuracy: ±2°
Offset impedance: 0.00 to 250.00 Ω in steps of 0.01
Pickup level: 0.015 to 30.000 pu in steps of 0.01
Dropout level: 97 to 98%
Operation time: <16 ms at 3 × pickup at 60 Hz
WATTMETRIC ZERO-SEQUENCE DIRECTIONAL
Measured power: zero-sequence
Number of elements: 2
Characteristic angle: 0 to 360° in steps of 1
Minimum power: 0.001 to 1.200 pu in steps of 0.001
Pickup level accuracy: ±1% or ±0.0025 pu, whichever is greater
Hysteresis: 3% or 0.001 pu, whichever is greater
Pickup delay: definite time (0 to 600.00 s in steps of
0.01), inverse time, or FlexCurve
Inverse time multiplier: 0.01 to 2.00 s in steps of 0.01
Curve timing accuracy: ±3.5% of operate time or ±1 cycle
(whichever is greater) from pickup to
operate
Operate time: <30 ms at 60 Hz
SENSITIVE DIRECTIONAL POWER
Measured power: 3-phase, true RMS
Number of stages: 2
Characteristic angle: 0 to 359° in steps of 1
Calibration angle: 0.00 to 0.95° in steps of 0.05
Minimum power: –1.200 to 1.200 pu in steps of 0.001
Pickup level accuracy: ±1% or ±0.001 pu, whichever is greater
Hysteresis: 2% or 0.001 pu, whichever is greater
Pickup delay: 0 to 600.00 s in steps of 0.01
Timer accuracy: ±3% of operate time or ±1/4 cycle
(whichever is greater)
Operate time: <50 ms
PHASE UNDERVOLTAGE
Voltage: Phasor only
Pickup level: 0.000 to 3.000 pu in steps of 0.001
Dropout level: 102 to 103% of pickup
Level accuracy: ±0.5% of reading from 10 to 208 V
Curve shapes: GE IAV Inverse;
Definite Time (0.1s base curve)
Curve multiplier: Time dial = 0.00 to 600.00 in steps of
0.01
Curve timing accuracy
at <0.90 x pickup: ±3.5% of operate time or ±1/2 cycle
(whichever is greater) from pickup to
operate
AUXILIARY UNDERVOLTAGE
Pickup level: 0.000 to 3.000 pu in steps of 0.001
Dropout level: 102 to 103% of pickup
Level accuracy: ±0.5% of reading from 10 to 208 V
Curve shapes: GE IAV Inverse, Definite Time
Curve multiplier: Time Dial = 0 to 600.00 in steps of 0.01
Curve timing accuracy
at <0.90 x pickup: ±3.5% of operate time or ±1/2 cycle
(whichever is greater) from pickup to
operate