46B6 Incipient Cable Fault Detector 1 Pickup 0.1 to 10 pu 0.01 F001 50
46B7 Incipient Cable Fault Detector 1 Mode 0 to 1 --- 1 F254 0 (Number of
Counts)
46B8 Incipient Cable Fault Detector 1 Trip Counts 1 to 10 --- 1 F001 2
46B9 Incipient Cable Fault Detector 1 Time Window 0 to 1000 s 0.01 F003 1000
46BB Incipient Cable Fault Detector 1 Reset Delay 0 to 65.535 s 0.001 F001 100
46BC Incipient Cable Fault Detector 1 Target 0 to 2 --- 1 F109 0 (Self-reset)
46BD Incipient Cable Fault Detector 1 Events 0 to 1 --- 1 F102 0 (Disabled)
46BE ...Repeated for Incipient Cable Fault Detector 2
Breaker Control (Read/Write Settings) (4 modules)
47D0 Breaker 1 Function 0 to 1 --- 1 F102 0 (Disabled)
47D1 Breaker 1 Name --- --- --- F206 “Bkr 1"
47D4 Breaker 1 Mode 0 to 1 --- 1 F157 0 (3-Pole)
47D5 Breaker 1 Open 0 to 4294967295 --- 1 F300 0
47D7 Breaker 1 Close 0 to 4294967295 --- 1 F300 0
47D9 Breaker 1 Phase A / Three-pole Closed 0 to 4294967295 --- 1 F300 0
47DB Breaker 1 Phase B Closed 0 to 4294967295 --- 1 F300 0
47DD Breaker 1 Phase C Closed 0 to 4294967295 --- 1 F300 0
47DF Breaker 1 External Alarm 0 to 4294967295 --- 1 F300 0
47E1 Breaker 1 Alarm Delay 0 to 65.535 s 0.001 F003 0
47E3 Breaker 1 Pushbutton Control 0 to 1 --- 1 F102 0 (Disabled)
47E4 Breaker 1 Manual Close Recall Time 0 to 4294967295 s 0.001 F003 0
47E6 Breaker 1 Out of Service 0 to 4294967295 --- 1 F300 0
47E8 Breaker 1 Block Open 0 to 4294967295 --- 1 F300 0
47EA Breaker 1 Block Close 0 to 4294967295 --- 1 F300 0
47EC Breaker 1 Phase A / Three-pole Opened 0 to 4294967295 --- 1 F300 0
47EE Breaker 1 Phase B Opened 0 to 4294967295 --- 1 F300 0
47F0 Breaker 1 Phase C Opened 0 to 4294967295 --- 1 F300 0
47F2 Breaker 1 Operate Time 0 to 65.535 s 0.001 F001 70
47F3 Breaker 1 Events 0 to 1 --- 1 F102 0 (Disabled)
47F4 Reserved 0 to 65535 s 1 F001 0
47F5 ...Repeated for Breaker 2
Demand (Read/Write Setting)
490A Demand Current Method 0 to 2 --- 1 F139 0 (Thermal
Exponential)
490B Demand Power Method 0 to 2 --- 1 F139 0 (Thermal
Exponential)
490C Demand Interval 0 to 5 --- 1 F132 2 (15 MIN)
490D Demand Input 0 to 4294967295 --- 1 F300 0
Demand (Read/Write Command)
490F Demand Clear Record 0 to 1 --- 1 F126 0 (No)
FlexCurves A and B (Read/Write Settings)
4910 FlexCurve A (120 items) 0 to 65535 ms 1 F011 0
4988 FlexCurve B (120 items) 0 to 65535 ms 1 F011 0
Modbus User Map (Read/Write Setting)
4A00 Modbus Address Settings for User Map (256 items) 0 to 65535 --- 1 F001 0
User Displays Settings (Read/Write Setting) (16 modules)
4C00 User-Definable Display 1 Top Line Text --- --- --- F202 “ “
4C0A User-Definable Display 1 Bottom Line Text --- --- --- F202 “ “
4C14 Modbus Addresses of Display 1 Items (5 items) 0 to 65535 --- 1 F001 0
4C19 Reserved (7 items) --- --- --- F001 0
4C20 ...Repeated for User-Definable Display 2
4C40 ...Repeated for User-Definable Display 3
4C60 ...Repeated for User-Definable Display 4
4C80 ...Repeated for User-Definable Display 5
Table B–10: MODBUS MEMORY MAP (Sheet 28 of 70)
ADDR REGISTER NAME RANGE UNITS STEP FORMAT DEFAULT