GE Multilin F60 Feeder Protection System B-19
APPENDIX B B.4 MEMORY MAPPING
B
2198 Breaker Flashover 1 Side 2 Source 0 to 6 --- 1 F211 0 (None)
2199 Breaker Flashover 1 Status Closed A 0 to 4294967295 --- 1 F300 0
219B Breaker Flashover 1 Status Closed B 0 to 4294967295 --- 1 F300 0
219D Breaker Flashover 1 Status Closed C 0 to 4294967295 --- 1 F300 0
219F Breaker Flashover 1 Voltage Pickup Level 0 to 1.5 pu 0.001 F001 850
21A0 Breaker Flashover 1 Voltage Difference Pickup Level 0 to 100000 V 1 F060 1000
21A2 Breaker Flashover 1 Current Pickup Level 0 to 1.5 pu 0.001 F001 600
21A3 Breaker Flashover 1 Pickup Delay 0 to 65.535 s 0.001 F001 100
21A4 Breaker Flashover 1 Supervision Phase A 0 to 4294967295 --- 1 F300 0
21A6 Breaker Flashover 1 Supervision Phase B 0 to 4294967295 --- 1 F300 0
21A8 Breaker Flashover 1 Supervision Phase C 0 to 4294967295 --- 1 F300 0
21AA Breaker Flashover 1 Block 0 to 4294967295 --- 1 F300 0
21AC Breaker Flashover 1 Events 0 to 1 --- 1 F102 0 (Disabled)
21AD Breaker Flashover 1 Target 0 to 2 --- 1 F109 0 (Self-Reset)
21AE Reserved (4 items) --- --- --- F001 0
21B2 ...Repeated for Breaker Flashover 2
Breaker Arcing Current Actual Values (Read Only Non-Volatile) (2 modules)
21E0 Breaker 1 Arcing Current Phase A 0 to 99999999 kA
2
-cyc 1 F060 0
21E2 Breaker 1 Arcing Current Phase B 0 to 99999999 kA
2
-cyc 1 F060 0
Breaker Arcing Current Actual Values (Read Only Non-Volatile) (2 modules)
21E4 Breaker 1 Arcing Current Phase C 0 to 99999999 kA
2
-cyc 1 F060 0
Breaker Arcing Current Actual Values (Read Only Non-Volatile) (2 modules)
21E6 Breaker 1 Operating Time Phase A 0 to 65535 ms 1 F001 0
21E7 Breaker 1 Operating Time Phase B 0 to 65535 ms 1 F001 0
Breaker Arcing Current Actual Values (Read Only Non-Volatile) (2 modules)
21E8 Breaker 1 Operating Time Phase C 0 to 65535 ms 1 F001 0
21E9 Breaker 1 Operating Time 0 to 65535 ms 1 F001 0
21EA ...Repeated for module number 2
Breaker Arcing Current Actual Values (Read Only Non-Volatile) (2 modules)
21EE ...Repeated for module number 2
Breaker Arcing Current Actual Values (Read Only Non-Volatile) (2 modules)
21F0 ...Repeated for module number 2
Breaker Arcing Current Actual Values (Read Only Non-Volatile) (2 modules)
21F2 ...Repeated for module number 2
Breaker Arcing Current Commands (Read/Write Command) (2 modules)
2224 Breaker 1 Arcing Current Clear Command 0 to 1 --- 1 F126 0 (No)
2225 Breaker 2 Arcing Current Clear Command 0 to 1 --- 1 F126 0 (No)
Passwords Unauthorized Access (Read/Write Command)
2230 Reset Unauthorized Access 0 to 1 --- 1 F126 0 (No)
Hi-Z (High Impedance Fault Detection) Commands (Read/Write Command)
2240 Hi-Z Clear Oscillography 0 to 1 --- 1 F126 0 (No)
2241 Hi-Z Oscillography Force Trigger 0 to 1 --- 1 F126 0 (No)
2242 Hi-Z Oscillography Force Algorithm Capture 0 to 1 --- 1 F126 0 (No)
2243 Hi-Z Reset Sigma Values 0 to 1 --- 1 F126 0 (No)
Hi-Z (High Impedance Fault Detection) Status (Read Only)
2250 Hi-Z Status 0 to 9 --- 1 F187 0 (NORMAL)
2251 Hi-Z Phase A Arc Confidence 0 to 100 --- 1 F001 0
2252 Hi-Z Phase B Arc Confidence 0 to 100 --- 1 F001 0
2253 Hi-Z Phase C Arc Confidence 0 to 100 --- 1 F001 0
2254 Hi-Z Neutral Arc Confidence 0 to 100 --- 1 F001 0
Hi-Z (High Impedance Fault Detection) Records (Read Only) (4 modules)
2260 Hi-Z Capture 1 Trigger Type 0 to 6 --- 1 F188 0 (NONE)
2261 Hi-Z Capture 1 Time 0 to 1 --- 1 F050 0
2263 ...Repeated for Hi-Z Capture 2
Table B–10: MODBUS MEMORY MAP (Sheet 11 of 70)
ADDR REGISTER NAME RANGE UNITS STEP FORMAT DEFAULT