B305 Wattmetric Ground Fault 1 Overcurrent Pickup 0.002 to 30.000 pu 0.001 F001 60
B306 Wattmetric Ground Fault 1 Overcurrent Pickup Delay 0 to 600 s 0.01 F001 20
B307 Wattmetric Ground Fault 1 Power Pickup 0.001 to 1.2 pu 0.001 F001 100
B308 Wattmetric Ground Fault 1 ECA 0 to 360 ° Lag 1 F001 0
B309 Wattmetric Ground Fault 1 Power Pickup Delay 0 to 600 s 0.01 F001 20
B30A Wattmetric Ground Fault 1 Curve 0 to 5 --- 1 F236 0 (Definite Time)
B30B Wattmetric Ground Fault 1 Multiplier 0.01 to 2 s 0.01 F001 100
B30C Wattmetric Ground Fault 1 Block 0 to 4294967295 --- 1 F300 0
B30E Wattmetric Ground Fault 1 Target 0 to 2 --- 1 F109 0 (Self-reset)
B30F Wattmetric Ground Fault 1 Events 0 to 1 --- 1 F102 0 (Disabled)
B310 Wattmetric Ground Fault 1 Reference Power 0.001 to 1.2 pu 0.001 F001 500
B311 Wattmetric Ground Fault 1 Reserved 0 to 1 --- 1 F001 0
B312 ...Repeated for Wattmetric Ground Fault 2
Wattmetric Ground Fault Actual Values (Read Only) (2 modules)
B360 Wattmetric Ground Fault 1 Operating Power 0.000 to 999999.999 W 0.001 F060 0
B362 ...Repeated for Wattmetric Ground Fault 2
IEC 61850 XSWI Configuration (Read/Write Setting) (24 modules)
B370 FlexLogic Operand for IEC 61850 XSWI.ST.Loc Status 0 to 4294967295 --- 1 F300 0
B373 ...Repeated for module number 2
B376 ...Repeated for module number 3
B379 ...Repeated for module number 4
B37C ...Repeated for module number 5
B37F ...Repeated for module number 6
B382 ...Repeated for module number 7
B385 ...Repeated for module number 8
B388 ...Repeated for module number 9
B38B ...Repeated for module number 10
B38E ...Repeated for module number 11
B391 ...Repeated for module number 12
B394 ...Repeated for module number 13
B397 ...Repeated for module number 14
B39A ...Repeated for module number 15
B39D ...Repeated for module number 16
B3A0 ...Repeated for module number 17
B3A3 ...Repeated for module number 18
B3A6 ...Repeated for module number 19
B3A9 ...Repeated for module number 20
B3AC ...Repeated for module number 21
B3AF ...Repeated for module number 22
B3B2 ...Repeated for module number 23
B3B5 ...Repeated for module number 24
IEC 61850 XSWI Configuration (Read/Write Command) (24 modules)
B372 Command to Clear XSWI OpCnt (Operation Counter) 0 to 1 --- 1 F126 0 (No)
IEC 61850 GGIO1 Configuration Settings (Read/Write Setting)
B400 Number of Status Indications in GGIO1 8 to 128 --- 8 F001 8
B402 IEC 61850 GGIO1 Indication FlexLogic operands (128
items)
0 to 4294967295 --- 1 F300 0
IEC 61850 Configurable GOOSE Transmission (Read/Write Setting) (8 modules)
B5A0 IEC 61850 Configurable GOOSE Function (GoEna) 0 to 1 --- 1 F102 1 (Enabled)
B5A1 IEC 61850 Configurable GOOSE ID --- --- --- F209 “GOOSEOut_x_”
B5C2 Configurable GOOSE Destination MAC Address --- --- --- F072 0
B5C5 IEC 61850 Configurable GOOSE VLAN Transmit Priority 0 to 7 --- 1 F001 4
B5C6 IEC 61850 Configurable GOOSE VLAN ID 0 to 4095 --- 1 F001 0
B5C7 IEC 61850 Configurable GOOSE ETYPE APPID 0 to 16383 --- 1 F001 0
Table B–10: MODBUS MEMORY MAP (Sheet 53 of 70)
ADDR REGISTER NAME RANGE UNITS STEP FORMAT DEFAULT