Menu 1 - INDOOR CLIMATE
Overview
1.1 - temperature1 - INDOOR CLIMATE
1.2 - ventilation
1.3.1 - heating1.3 - scheduling
1.3.3 - ventilation
1.9.1.1 - heating curve1.9 - advanced
1.9.2 - external adjustment
1.9.3 - min. flow line temp.
1.9.4 - room sensor settings
1.9.6 - fan return time
1.9.7 - own curve
1.9.8 - point offset
1.9.9 - night cooling
Sub-menus
For the menu INDOOR CLIMATE there are several sub-
menus. Status information for the relevant menu can
be found on the display to the right of the menus.
temperature Setting the temperature for the climate
system. The status information shows the set values
for the climate system.
ventilation Setting the fan speed. The status informa-
tion shows the selected setting.
scheduling Scheduling heating and ventilation. Status
information "set" is displayed if you set a schedule but
it is not active now, "holiday setting" is displayed if the
vacation schedule is active at the same time as the
schedule (the vacation function is prioritised), "active"
displays if any part of the schedule is active, otherwise
it displays "off".
advanced Setting of heat curve, adjusting with extern-
al contact, minimum value for supply temperature,
room sensor and night cooling.
Menu 1.1 - temperature
Set the temperature (with room sensors installed
and activated):
heating
Setting range: 5 – 30 °C
Default value: 20
The value in the display appears as a temperature in
°C if the climate system is controlled by a room sensor.
Caution
A slow heat-releasing heating system, such as
for example, underfloor heating, may not be
suitable for control using the heat pump's
room sensor.
To change the room temperature, use the control knob
to set the desired temperature in the display. Confirm
the new setting by pressing the OK button. The new
temperature is shown on the right-hand side of the
symbol in the display.
Setting the temperature (without room sensors
activated):
Setting range: -10 to +10
Default value: -1
The display shows the set values for heating (curve
offset). To increase or reduce the indoor temperature,
increase or reduce the value on the display.
Use the control knob to set a new value. Confirm the
new setting by pressing the OK button.
The number of steps the value has to be changed to
achieve a degree change of the indoor temperature
depends on the heating installation. One step is usually
enough but in some cases several steps may be re-
quired.
Setting the desired value. The new value is shown on
the right-hand side of the symbol in the display.
Caution
An increase in the room temperature can be
slowed by the thermostats for the radiators or
under floor heating. Therefore, open the
thermostats fully, except in those rooms where
a cooler temperature is required, e.g. bed-
rooms.
If the exhaust air temperature falls below 16
°C the compressor is blocked and electric addi-
tional heat is permitted. Heat is not recovered
from the exhaust air when the compressor is
blocked.