Setting the ventilation
Ventilation must be set according to applicable stand-
ards. The setting is made in menu 5.1.5.
Even if ventilation is roughly set at installation it is im-
portant that a ventilation adjustment is ordered and
permitted.
NOTE
Order a ventilation adjustment to complete
the setting.
Fan diagram F370
Flow (l/s)
Available
pressure
(Pa)
0
50
100
150
200
250
300
350
400
450
0 20 40 60 80 100 120
Flöde (l/s)
30%
40%
50%
60%
70%
20%
10%
80%
90%/100%
Tillgängligt tryck (Pa)
0
20
40
60
80
100
120
140
0 20 40 60 80 100 120
Effekt
(watt)
40%
50%
80%
90%/100%
30%
10%
20%
60%
70%
Luftflöde (l/s)
Power direct current fan
Power output
(W)
Airflow
(l/s)
Commissioning without fan
The heat pump can be run without recovery, as only
an electric boiler, to produce heat and hot water, for
example before the ventilation installation is complete.
Enter menu 4.2 - "op. mode" and select "add. heat only"
Enter menu 5.1.5 - "fan sp. exhaust air" and reduce the
fan speed to 0%.
NOTE
Select operating mode "auto" or "manual"
when the heat pump is to run on recovery
again.
NIBE™ F370Chapter 6 | Commissioning and adjusting32