Setting the pump speed
The speed of the circulation pump (GP1) is set using
the switch (GP1-SF4) on the pump so that it achieves
the projected flow for the house.
Tillgängligt
tryck
(kPa)
Luftflöde
(l/s)
0
0 0,05 0,11 0,16 0,22 0,27 0,33 0,38
10
20
30
40
50
60
I
II
III
Capacity circulation pump
Pressure
(kPa)
Flow (l/s)
Capacity circulation pump
Effekt
(watt)
Flöde
(l/s)
0
0 0,05 0,11 0,16 0,22 0,27 0,33 0,38
5
10
15
20
25
30
35
40
45
50
I
II
III
Power output
(W)
Flow (l/s)
Output circulation pump
Post-adjustment, venting
Air is initially released from the hot water and venting
may be necessary. If gurgling sounds can be heard from
the heat pump or climate system, the entire system will
require additional venting. Vent the heat pump
through venting valve (QM21). When venting, F370
must be off.
33Chapter 6 | Commissioning and adjustingNIBE™ F370