Setting the pump speed
The speed of the circulation pump (GP1) is set using
the switch (GP1-SF4) on the pump so that it achieves
the projected flow for the house.
L
EK
L
EK
GP1-SF4
Tillgängligt
tryck
(kPa)
Luftflöde
(l/s)
0
0 0,05 0,11 0,16 0,22 0,27 0,33 0,38
10
20
30
40
50
60
I
II
III
Capacity circulation pump
Pressure
(kPa)
Flow (l/s)
Capacity circulation pump
Effekt
(watt)
Flöde
(l/s)
0
0 0,05 0,11 0,16 0,22 0,27 0,33 0,38
5
10
15
20
25
30
35
40
45
50
I
II
III
Power output
(W)
Flow (l/s)
Output circulation pump
Post-adjustment, venting
Air is initially released from the hot water and venting
may be necessary. If gurgling sounds can be heard from
the heat pump or climate system, the entire system will
require additional venting. Vent the heat pump
through venting valve (QM21). When venting, F370
must be off.
33Chapter 6 | Commissioning and adjustingNIBE™ F370

Other manuals for Nibe F370

Questions and Answers:

Question and Answer IconNeed help?

Do you have a question about the Nibe F370 and is the answer not in the manual?

Nibe F370 Specifications

General IconGeneral
TypeExhaust Air Heat Pump
RefrigerantR290
Energy classA++
Energy Efficiency Class (Space Heating, 35°C)A++
Energy Efficiency Class (Space Heating, 55°C)A+
ApplicationResidential
Hot Water Tank Volume170 l
Heating Power8.5 kW

Related product manuals