5-76 F35 MULTIPLE FEEDER PROTECTION SYSTEM – INSTRUCTION MANUAL
PRODUCT SETUP CHAPTER 5: SETTINGS
5
RxGOOSE DPS1 Member
Range: 1 to 64 in steps of 1
Default: 1
This setting selects the GOOSE message member that drives the RxGOOSE DPS1 FlexLogic operand. A setting of 1 selects 
the first member, 2 selects the second member, and so on. Entering a number greater than the number of members in 
the message and entering the number of a member that is not a Dbpos results in the RxGOOSE DPS1 FlexLogic operand 
assuming its default state. In the case that the member is a structure containing more than one Dbpos, the Subscribed 
to column identifies the particular Dbpos subscribed to.
RxGOOSE DSP1 DEFAULT STATE
Range: Intermediate-state, Off, On, Bad-state, Latest
Default: Latest
This setting selects the logic state for the data attribute @Master/GGIO3.IndPos01.stVal and the DPS FlexLogic operands 
when the UR has just completed start-up and the selected RxGOOSE has not yet received a message, and when the 
RxGOOSE has lost its connection with the publisher. When this setting is selected to Latest, the value of @Master/
GGIO3.IndPosψψ.stVal is Intermediate-state when the UR has just completed start-up and the selected RxGOOSE has 
not yet received a message, and the latest received value when the RxGOOSE loses its connectivity with the publisher.
RxGOOSE DPS1 EVENTS
Range: Disabled, Enabled
Default: Disabled
This setting selects whether Off to On transitions of the RxGOOSE DPS1 FlexLogic operands are recorded by the event 
recorder. If set to Enabled, Off to On transitions are recorded. On to Off transitions are never recorded, even if events are 
enabled.
RxGOOSE analog inputs
Navigate to Settings > Product Setup > Communications > IEC 61850 > GOOSE > RxGOOSE > RxGOOSE Analog Inputs.
There are Add IED and Remove IED buttons. The Add IED button allows SCL files to be used, including ICD, CID, and SCD 
(supported in version 7.40 and later). When the file format is SCD, the system lists all IEDs inside the SCD file and lets the 
user select the ones to add.
Figure 5-31: RxGOOSE Analog Inputs panel
There are 32 RxGOOSE analog inputs.