CHAPTER 5: SETTINGS GROUPED ELEMENTS
F35 MULTIPLE FEEDER PROTECTION SYSTEM – INSTRUCTION MANUAL 5-247
5
Figure 5-131: Ground IOC1 logic
5.7.7 Negative sequence current
5.7.7.1 Menu
SETTINGS  GROUPED ELEMENTS SETTING GROUP 1(6)  NEGATIVE SEQUENCE CURRENT
For information on the negative sequence time overcurrent curves, see the Inverse Time Overcurrent Curves section
earlier.
5.7.7.2 Negative sequence time overcurrent (ANSI 51Q, IEC PTOC)
SETTINGS  GROUPED ELEMENTS SETTING GROUP 1(6)  NEGATIVE SEQUENCE CURRENT NEG SEQ TOC1
These elements measure the current that is connected to the ground channel of a CT/VT module. The conversion
range of a standard channel is from 0.02 to 46 times the CT rating.
This channel can be equipped with a standard or sensitive input. The conversion range of a sensitive channel is
from 0.002 to 4.6 times the CT rating.
NEGATIVE SEQUENCE
CURRENT
NEG SEQ TOC1
See below
NEG SEQ TOC2
NEG SEQ IOC1
See page 5-248
NEG SEQ IOC2
NEG SEQ TOC1
NEG SEQ TOC1
FUNCTION: Disabled
Range: Disabled, Enabled
NEG SEQ TOC1 SIGNAL
SOURCE: SRC 1
Range: SRC 1, SRC 2, SRC 3, SRC 4, SRC 5, SRC 6
NEG SEQ TOC1
PICKUP: 1.000 pu
Range: 0.020 to 30.000 pu in steps of 0.001
NEG SEQ TOC1
CURVE: IEEE Mod Inv
Range: see Overcurrent Curve Types table
NEG SEQ TOC1
TD MULTIPLIER: 1.00
Range: 0.00 to 600.00 in steps of 0.01

Table of Contents

Questions and Answers:

Question and Answer IconNeed help?

Do you have a question about the GE F35 and is the answer not in the manual?

GE F35 Specifications

General IconGeneral
Frequency50/60 Hz
Device FunctionProtection Relay
Communication ProtocolsDNP3
TypeDigital Protection Relay
Current Rating5 A
Protection FunctionsOvercurrent

Related product manuals