5-306 F35 MULTIPLE FEEDER PROTECTION SYSTEM – INSTRUCTION MANUAL
CONTROL ELEMENTS CHAPTER 5: SETTINGS
5
Figure 5-170: Cold load pickup logic
5.8.12 PID regulator
SETTINGS  CONTROL ELEMENTS  PID REGULATOR  PID 1(4) REGULATOR
PID 1
REGULATOR
PID 1
FUNCTION: Disabled
Range: Enabled, Disabled
PID 1 SAMPLE TIME:
0.05 s
Range: 0.05 to 30.00 s in steps of 0.01
PID 1 PROCESS
SIGNAL: Off
Range: Off, any FlexAnalog parameter
PID 1 SETPOINT
SIGNAL: 0.00
Range: -99999.99 to 99999.99 in steps of 0.01
PID 1 TRACKING SIGNAL:
Off
Range: Off, any FlexAnalog parameter
PID 1 PROPORTIONAL
GAIN: 1.00
Range: 0.01 to 100.00 in steps of 0.01
PID 1 SETPOINT
WEIGHTING: 1.00
Range: 0.01 to 1.00 in steps of 0.01
PID 1 INTEG. TIME
CONST.: 1.00 sec
Range: 0.00 to 600.00 s in steps of 0.01
PID 1 ANTIWINDUP:
Disabled
Range: Enabled, Disabled
PID 1 AW TIME CONST.:
1.00 sec
Range: 0.00 to 600.00 s in steps of 0.01
PID 1 DERIV. TIME
CONST.: 1.00 s
Range: 0.00 to 600.00 s in steps of 0.01
PID 1 DERIVATIVE
LIMIT: 10
Range: 1 to 20 in steps of 1