CHAPTER 6: ACTUAL VALUES RECORDS
F35 MULTIPLE FEEDER PROTECTION SYSTEM – INSTRUCTION MANUAL 6-23
6
The RxGOOSE Analog values display in this menu. The RxGOOSE Analog values are received via IEC 61850 GOOSE
messages sent from other devices.
6.4.6 Wattmetric ground fault
ACTUAL VALUES METERING WATTMETRIC GROUND FAULT 1(4)
This menu displays the wattmetric zero-sequence directional element operating power values.
6.4.7 Transducer inputs/outputs
ACTUAL VALUES METERING TRANSDUCER I/O DCMA INPUTS DCMA INPUT xx
Actual values for each DCmA input channel that is enabled are displayed with the top line as the programmed channel ID
and the bottom line as the value followed by the programmed units.
ACTUAL VALUES METERING TRANSDUCER I/O RTD INPUTS RTD INPUT xx
Actual values for each RTD input channel that is enabled are displayed with the top line as the programmed channel ID
and the bottom line as the value.
6.5 Records
6.5.1 Fault reports
ACTUAL VALUES RECORDS FAULT REPORTS FAULT REPORT 1(15)
The F35 is provided with optional GOOSE communications capability. This feature is specified as a software
option at the time of ordering. See the Order Codes section of chapter 2 for details.
WATTMETRIC
GROUND FAULT 1
WATT GND FLT 1:
0.000 W
DCMA INPUT xx
DCMA INPUT xx
0.000 mA
RTD INPUT xx
RTD INPUT xx
-50 °C
NO FAULTS TO REPORT
or
FAULT REPORT 1
FAULT 1
LINE ID: SRC 1
Range: SRC 1, SRC 2, SRC 3, SRC 4, SRC 5, SRC 6
FAULT 1 DATE:
2000/08/11
Range: YYYY/MM/DD
FAULT 1 TIME:
00:00:00.000000
Range: HH:MM:SS.ssssss
FAULT 1 TYPE:
ABG
Range: not available if the source VTs are in the
“Delta” configuration
FAULT 1 LOCATION
00.0 km
Range: not available if the source VTs are in the
“Delta” configuration