CHAPTER 5: SETTINGS GROUPED ELEMENTS
F35 MULTIPLE FEEDER PROTECTION SYSTEM – INSTRUCTION MANUAL 5-227
5
Figure 5-122: Non-volatile latch operation table (N = 1 to 16) and logic
5.7 Grouped elements
5.7.1 Overview
Each protection element can be assigned up to six sets of settings with designations 1 to 6. The performance of these
elements is defined by the active setting group at a given time. Multiple setting groups allow the user to conveniently
change protection settings for different operating situations (for example, altered power system configuration or season of
the year). The active setting group can be preset or selected in the
SETTING GROUPS menu (see the Control Elements section
later in this chapter). See also the Introduction to Elements section at the beginning of this chapter.
5.7.2 Setting group 1
SETTINGS  GROUPED ELEMENTS SETTING GROUP 1(6)
Latch n type Latch n
set
Latch n
reset
Latch n
on
Latch n
off
Reset
Dominant
ON OFF ON OFF
OFF OFF Previous
State
Previous
State
ON ON OFF ON
OFF ON OFF ON
Set
Dominant
ON OFF ON OFF
ON ON ON OFF
OFF OFF Previous
State
Previous
State
OFF ON OFF ON
SETTING GROUP 1
PHASE CURRENT
See below
NEUTRAL CURRENT
See page 5-237
WATTMETRIC
GROUND FAULT
See page 5-240
GROUND CURRENT
See page 5-244

Table of Contents