CHAPTER 6: ACTUAL VALUES PRODUCT INFORMATION
F35 MULTIPLE FEEDER PROTECTION SYSTEM – INSTRUCTION MANUAL 6-27
6
6.5.5 Breaker maintenance
ACTUAL VALUES  RECORDS  MAINTENANCE BREAKER 1(6)
There is an identical menu for each of the breakers.
The
BKR 1 ACC ARCING AMP values are in units of kA
2
-cycles. See the COMMANDS  CLEAR RECORDS menu for clearing
breaker arcing current records.
The
BREAKER OPERATING TIME is defined as the slowest operating time of breaker poles that were initiated to open.
All of the values are stored in non-volatile memory and retained with power cycling.
6.6 Product information
6.6.1 Model information
ACTUAL VALUES  PRODUCT INFO MODEL INFORMATION
BREAKER 1
BKR 1 ACC ARCING AMP
φA: 0.00 kA2-cyc
BKR 1 ACC ARCING AMP
φB: 0.00 kA2-cyc
BKR 1 ACC ARCING AMP
φC: 0.00 kA2-cyc
BKR 1 OPERATING TIME
φA: 0 ms
BKR 1 OPERATING TIME
φB: 0 ms
BKR 1 OPERATING TIME
φC: 0 ms
BKR 1 OPERATING
TIME: 0 ms
BKR 1 ARCING AMP φA:
0.00 kA2-cyc
BKR 1 ARCING AMP φB:
0.00 kA2-cyc
BKR 1 ARCING AMP φC:
0.00 kA2-cyc
BKR 1 AMP MAX φA:
0.00 kA
BKR 1 AMP MAX φB:
0.00 kA
BKR 1 AMP MAX φC:
0.00 kA
MODEL INFORMATION
ORDER CODE LINE 1:
F35-A00-AAA-A0A-A0A-
Range: standard GE order code format
ORDER CODE LINE 2:
A0A-A0A-A0A
Range: up to 20 alphanumeric characters
ORDER CODE LINE 3: Range: up to 20 alphanumeric characters

Table of Contents

Questions and Answers:

Question and Answer IconNeed help?

Do you have a question about the GE F35 and is the answer not in the manual?

GE F35 Specifications

General IconGeneral
Frequency50/60 Hz
Device FunctionProtection Relay
Communication ProtocolsDNP3
TypeDigital Protection Relay
Current Rating5 A
Protection FunctionsOvercurrent

Related product manuals