5-150 F35 MULTIPLE FEEDER PROTECTION SYSTEM – INSTRUCTION MANUAL
PRODUCT SETUP CHAPTER 5: SETTINGS
5
The F35 maintains two times: local time and Universal Coordinated Time (UTC). Local time can be provided by IRIG-B
signals. UTC time is provided by SNTP servers.
The real-time clock (RTC) and time stamps reported in historical records and communication protocols can be incorrect if
the Local Time settings are not configured properly.
See the IRIG-B section in the Installation chapter for guidance on these settings when using an IRIG-B source that sets the
IRIG-B control bits according to IEEE Std 1344-1995.
LOCAL TIME OFFSET FROM UTC — Used to specify the local time zone offset from UTC (Greenwich Mean Time) in hours. Time
zones in the eastern hemisphere have positive values; time zones in the western hemisphere have negative values. A value
of zero causes the relay to use UTC for local time. This setting has two uses. When the system RTC is synchronized with a
communications protocol providing only local time or it is free-running, the offset setting is used to calculate UTC from the
local time these provide. When the RTC is synchronized with a communications protocol providing only UTC (such as PTP or
SNTP), the time offset setting is used to determine local time from the UTC provided. PTP
ALTERNATE_TIME_OFFSET_INDICATOR TLVs are not used to calculate local time.
DAYLIGHT SAVINGS TIME and DST — Can be used to allow the relay to follow the DST rules of the local time zone. Note that
when IRIG-B time synchronization is active, the local time in the IRIG-B signal contains any daylight savings time offset and
so the DST settings are ignored.
5.3.8 Fault reports
SETTINGS  PRODUCT SETUP  FAULT REPORTS  FAULT REPORT 1(5)
DST START DAY:
Sunday
Range: Sunday to Saturday (all days of the week)
DST START DAY
INSTANCE: First
Range: First, Second, Third, Fourth, Last
DST START HOUR:
2:00
Range: 0:00 to 23:00 in steps of one hour
DST STOP MONTH:
January
Range: January to December (all months)
DST STOP DAY:
Sunday
Range: Sunday to Saturday (all days of the week)
DST STOP DAY
INSTANCE: First
Range: First, Second, Third, Fourth, Last
DST STOP HOUR:
2:00
Range: 0:00 to 23:00 in steps of one hour
FAULT REPORT 1
FAULT REPORT 1
SOURCE: SRC 1
Range: SRC 1, SRC 2, SRC 3, SRC 4, SRC 5, SRC 6
FAULT REPORT 1 TRIG:
Off
Range: FlexLogic operand
FAULT REPORT 1 Z1
MAG: 3.00 Ω
Range: 0.01 to 250.00 ohms in steps of 0.01
FAULT REPORT 1 Z1
ANGLE: 75°
Range: 25 to 90° in steps of 1
FAULT REPORT 1 Z0
MAG: 9.00 Ω
Range: 0.01 to 650.00 ohms in steps of 0.01
FAULT REPORT 1 Z0
ANGLE: 75°
Range: 25 to 90° in steps of 1
FAULT REPORT 1 Z0M
MAG: 0.00 Ω
Range: 0.00 to 650.00 ohms in steps of 0.01

Table of Contents

Questions and Answers:

Question and Answer IconNeed help?

Do you have a question about the GE F35 and is the answer not in the manual?

GE F35 Specifications

General IconGeneral
Frequency50/60 Hz
Device FunctionProtection Relay
Communication ProtocolsDNP3
TypeDigital Protection Relay
Current Rating5 A
Protection FunctionsOvercurrent

Related product manuals