2-24 F35 MULTIPLE FEEDER PROTECTION SYSTEM – INSTRUCTION MANUAL
SPECIFICATIONS CHAPTER 2: PRODUCT DESCRIPTION
2
2.5.4 Metering
RMS CURRENT: PHASE, NEUTRAL, AND GROUND
Accuracy at
0.1 to 2.0 × CT rating: ±0.25% of reading or ±0.1% of rated (whichever is greater)
> 2.0 × CT rating: ±1.0% of reading
RMS VOLTAGE
Accuracy: ±0.5% of reading from 10 to 208 V
REAL POWER (WATTS)
Accuracy at 0.1 to 1.5 x CT rating and 0.8 to 1.2 x VT rating:
±1.0% of reading at –1.0 ≤ PF < –0.8 and 0.8 < PF ≤ 10
REACTIVE POWER (VARS)
Accuracy at 0.1 to 1.5 x CT rating and 0.8 to 1.2 x VT rating:
±1.0% of reading at –0.2 ≤ PF ≤ 0.2
APPARENT POWER (VA)
Accuracy at 0.1 to 1.5 x CT rating and 0.8 to 1.2 x VT rating:
±1.0% of reading
WATT-HOURS (POSITIVE AND NEGATIVE)
Accuracy: ±2.0% of reading
Range: ±0 to 1 × 10
6
MWh
Parameters: three-phase only
Update rate: 50 ms
VAR-HOURS (POSITIVE AND NEGATIVE)
Accuracy: ±2.0% of reading
Range: ±0 to 1 × 10
6
Mvarh
Parameters: three-phase only
Update rate: 50 ms
CURRENT HARMONICS
Harmonics: 2nd to 25th harmonic: per phase, displayed as a % of f
1
(fundamental frequency phasor)
THD: per phase, displayed as a % of f
1
Accuracy:
HARMONICS: 1. f
1
> 0.4pu: (0.20% + 0.035% / harmonic) of reading or 0.15% of 100%, whichever is greater
2. f
1
< 0.4pu: as above plus %error of f
1
THD: 1. f
1
> 0.4pu: (0.25% + 0.035% / harmonic) of reading or 0.20% of 100%, whichever is greater
2. f
1
< 0.4pu: as above plus %error of f
1
VOLTAGE HARMONICS
Harmonics: 2nd to 25th harmonic: per phase, displayed as a % of f
1
(fundamental frequency phasor)
THD: per phase, displayed as a % of f
1
Accuracy:
HARMONICS: 1. f
1
> 0.4pu: (0.20% + 0.035% / harmonic) of reading or 0.15% of 100%, whichever is greater
2. f
1
< 0.4pu: as above plus %error of f
1
THD: 1. f
1
> 0.4pu: (0.25% + 0.035% / harmonic) of reading or 0.20% of 100%, whichever is greater
2. f
1
< 0.4pu: as above plus %error of f
1
FREQUENCY
Accuracy at
V = 0.8 to 1.2 pu: ±0.001 Hz (when voltage signal is used for frequency measurement)
I = 0.1 to 0.25 pu: ±0.005 Hz
I > 0.25 pu: ±0.02 Hz (when current signal is used for frequency measurement)