6.3.20 Incipient fault detector
ACTUAL VALUES STATUS  INCIPIENT FAULT INCIPIENT FAULT 1(6)
The number of detected incipient faults for each incipient fault element are displayed here for each phase. These values
can be reset to zero with the
COMMANDS  CLEAR RECORDS  CLEAR INCIPENT FAULT COUNTERS command.
6.3.21 Remaining connection status
ACTUAL VALUES STATUS  COMM STATUS REMAINING CONNECT
These values specify the remaining number of TCP connections still available for each protocol. The display depends on the
options applicable to your device. Each time a connection is used, the remaining number of connections decrements.
When released, the remaining number of connections increments. If no connection is made over the specific protocol, the
number equals the maximum number available for the specific protocol.
For example, the maximum number of Modbus TCP connections is 4. Once an EnerVista session is opened on a computer
connected to the UR over Ethernet, the Modbus TCP status shows 3. If the EnerVista application is closed, the Modbus TCP
status shows 4.
For the graphical front panel, the remaining connections refer to TCP connections only.
MMS TCP — The number of IEC 61850 connections remaining.
6.3.22 Parallel Redundancy Protocol (PRP)
The Parallel Redundancy Protocol (PRP) defines a redundancy protocol for high availability in substation automation
networks.
ACTUAL VALUES STATUS  PRP STATUS
INCIPIENT FAULT 1
INCIPIENT FAULT 1
PH A FAULTS: 0
Range: 0 to 65535 in steps of 1
INCIPIENT FAULT 1
PH B FAULTS: 0
Range: 0 to 65535 in steps of 1
INCIPIENT FAULT 1
PH C FAULTS: 0
Range: 0 to 65535 in steps of 1
COMM STATUS
REMAINING CONNECT
MMS TCP(max 5)
5
Range: 0 to 5
MODBUS TCP (max 4)
4
Range: 0 to 4
DNP TCP(max 2)
2
Range: 0 to 2
IEC-104 TCP(max 2)
2
Range: 0 to 2
SFTP (max 4)
4
Range: 0 to 4
PRP STATUS
Total Rx Port A:
0
Range: 0 to 4G, blank if PRP disabled
Total Rx Port B:
0
Range: 0 to 4G, blank if PRP disabled
Mismatches Port A:
0
Range: 0 to 4G, blank if PRP disabled
Mismatches Port B:
0
Range: 0 to 4G, blank if PRP disabled

Table of Contents

Questions and Answers:

Question and Answer IconNeed help?

Do you have a question about the GE F35 and is the answer not in the manual?

GE F35 Specifications

General IconGeneral
Frequency50/60 Hz
Device FunctionProtection Relay
Communication ProtocolsDNP3
TypeDigital Protection Relay
Current Rating5 A
Protection FunctionsOvercurrent

Related product manuals