6-22 F35 MULTIPLE FEEDER PROTECTION SYSTEM – INSTRUCTION MANUAL
METERING CHAPTER 6: ACTUAL VALUES
6
6.4.3 Tracking frequency
ACTUAL VALUES  METERING  TRACKING FREQUENCY
The tracking frequency displays here. The frequency is tracked based on the selection of the reference source with the
FREQUENCY AND PHASE REFERENCE setting in the SETTINGS  SYSTEM SETUP  POWER SYSTEM menu. See the Power
System section of chapter 5 for details.
6.4.4 FlexElements
ACTUAL VALUES  METERING  FLEXELEMENTS FLEXELEMENT 1(16)
The operating signals for the FlexElements are displayed in pu values using the following definitions of the base units.
Table 6-2: FlexElement base units
6.4.5 RxGOOSE analogs
ACTUAL VALUES  METERING  RxGOOSE Analogs
Voltage harmonics are calculated only for Wye connected phase VTs. Ensure that the
SYSTEM SETUP AC INPUTS
 VOLTAGE BANK F5  PHASE VT XX CONNECTION
setting is “Wye” to enable voltage harmonics metering.
TRACKING FREQUENCY
TRACKING FREQUENCY:
60.00 Hz
FLEXELEMENT 1
FLEXELEMENT 1
OpSig: 0.000
Base unit Description
BREAKER ACC ARCING AMPS
(Brk X Acc Arc Amp A, B, and C)
BASE = 2000 kA
2
× cycle
BREAKER ARCING AMPS
(Brk X Arc Amp A, B, and C)
BASE = 1 kA
2
× cycle
DCmA BASE = maximum value of the DCMA INPUT MAX setting for the two transducers configured
under the +IN and –IN inputs.
FAULT LOCATION BASE = Line Length as specified in Fault Report
FREQUENCY f
BASE
= 1 Hz
PHASE ANGLE ϕ
BASE
= 360 degrees (see the UR angle referencing convention)
POWER FACTOR PF
BASE
= 1.00
RTDs BASE = 100°C
SOURCE CURRENT I
BASE
= maximum nominal primary RMS value of the +IN and –IN inputs
SOURCE ENERGY
(Positive and Negative Watthours,
Positive and Negative Varhours)
E
BASE
= 10000 MWh or MVAh, respectively
SOURCE POWER P
BASE
= maximum value of V
BASE
× I
BASE
for the +IN and –IN inputs
SOURCE THD & HARMONICS BASE = 1%
SOURCE VOLTAGE V
BASE
= maximum nominal primary RMS value of the +IN and –IN inputs
RxGOOSE
Analogs
RxGOOSE Analog 1
0.000
RxGOOSE Analog 32
0.000

Table of Contents

Questions and Answers:

Question and Answer IconNeed help?

Do you have a question about the GE F35 and is the answer not in the manual?

GE F35 Specifications

General IconGeneral
Frequency50/60 Hz
Device FunctionProtection Relay
Communication ProtocolsDNP3
TypeDigital Protection Relay
Current Rating5 A
Protection FunctionsOvercurrent

Related product manuals