CHAPTER 6: ACTUAL VALUES METERING
F35 MULTIPLE FEEDER PROTECTION SYSTEM – INSTRUCTION MANUAL 6-21
6
6.4.2.10 Current harmonics and THD metering
ACTUAL VALUES  METERING SOURCE SRC 1  CURRENT HARMONICS
This menu displays metered current harmonics values. The "SRC 1" text is replaced by the name was programmed for the
associated source (see
SETTINGS  SYSTEM SETUP  SIGNAL SOURCES). Current harmonics are measured for each source
for the total harmonic distortion (THD) and 2nd to 25th harmonics per phase.
6.4.2.11 Voltage harmonics and THD metering
ACTUAL VALUES  METERING SOURCE SRC 1  VOLTAGE HARMONICS
This menu displays metered voltage harmonics values. The “SRC 1” text is replaced by the programmed name for the
associated source (see the
SETTINGS  SYSTEM SETUP  SIGNAL SOURCES menu).
To extract the 2nd to 25th voltage harmonics, each harmonic is computed on a per-phase basis, where:
N = 64 is the number of samples per cycle
ω
0
= 2πf is the angular frequency based on the system frequency (50 or 60 Hz)
k = 1, 2,..., N – 1 is the index over one cycle for the Fast Fourier Transform (FFT)
m is the last sample number for the sliding window
h = 1, 2,..., 25 is the harmonic number
The short-time Fourier transform is applied to the unfiltered signal:
Eq. 6-3
The harmonics are a percentage of the fundamental signal obtained as a ratio of harmonic amplitude to fundamental
amplitude multiplied by 100%. The total harmonic distortion (THD) is the ratio of the total harmonic content to the
fundamental:
Eq. 6-4
CURRENT HARMONICS
SRC 1
SRC 1 THD Ia: 0.0
Ib: 0.0 Ic: 0.0%
SRC 1 2ND Ia: 0.0
Ib: 0.0 Ic: 0.0%
SRC 1 3RD Ia: 0.0
Ib: 0.0 Ic: 0.0%
SRC 1 25TH Ia: 0.0
Ib: 0.0 Ic: 0.0%
VOLTAGE HARMONICS
SRC 1
SRC 1 THD Va: 0.0
Vb: 0.0 Vc: 0.0%
SRC 1 2ND Va: 0.0
Vb: 0.0 Vc: 0.0%
SRC 1 3RD Va: 0.0
Vb: 0.0 Vc: 0.0%
SRC 1 25TH Va: 0.0
Vb: 0.0 Vc: 0.0%