6-6 F35 MULTIPLE FEEDER PROTECTION SYSTEM – INSTRUCTION MANUAL
STATUS CHAPTER 6: ACTUAL VALUES
6
The present state of the contact outputs is shown here. The first line of a message display indicates the ID of the contact
output. For example, ‘Cont Op 1’ refers to the contact output in terms of the default name-array index. The second line of
the display indicates the logic state of the contact output.
For form-A contact outputs, the state of the voltage and current detectors is displayed as Off, VOff, IOff, On, IOn, and VOn.
For form-C contact outputs, the state is displayed as Off or On.
6.3.7 Virtual outputs
ACTUAL VALUES STATUS  VIRTUAL OUTPUTS
The present state of up to 96 virtual outputs is shown here. The first line of a message display indicates the ID of the virtual
output. For example, ‘Virt Op 1’ refers to the virtual output in terms of the default name-array index. The second line of the
display indicates the logic state of the virtual output, as calculated by the FlexLogic equation for that output.
6.3.8 Autoreclose
ACTUAL VALUES STATUS  AUTORECLOSE AUTORECLOSE 1(6)
This menu displays the reclosure shot count.
6.3.9 RxGOOSE status
ACTUAL VALUES STATUS  RxGOOSE STATUS
The
All RxGOOSE Online actual value does not consider RxGOOSE that are not configured or are not used by any RxGOOSE
Input.
Cont Op xx
Off
Range: On, Off, VOff, VOn, IOn, IOff
VIRTUAL OUTPUTS
Virt Op 1
Off
Range: On, Off
Virt Op 96
Off
Range: On, Off
AUTORECLOSE 1
AUTORECLOSE 1
SHOT COUNT: 0
Range: 0, 1, 2, 3, 4
RxGOOSE
STATUS
All RxGOOSE Online:
Yes
Range: Yes, No
RxGOOSE 1 Status:
Offline
Range: Online, Offline
RxGOOSE 64 Status:
Offline
Range: Online, Offline
The F35 is provided with optional IEC 61850 capability. This feature is specified as a software option at the time
of ordering. See the Order Codes section of chapter 2 for details.

Table of Contents

Questions and Answers:

Question and Answer IconNeed help?

Do you have a question about the GE F35 and is the answer not in the manual?

GE F35 Specifications

General IconGeneral
Frequency50/60 Hz
Device FunctionProtection Relay
Communication ProtocolsDNP3
TypeDigital Protection Relay
Current Rating5 A
Protection FunctionsOvercurrent

Related product manuals