CHAPTER 5: SETTINGS PRODUCT SETUP
F35 MULTIPLE FEEDER PROTECTION SYSTEM – INSTRUCTION MANUAL 5-97
5
Latitude
Range: -90.000 to 90.000 degrees in steps of 0.001 degree
Default: 0.000 deg
The value entered sets the value of the data attribute <LDName>/LPHD1.PhyNam.latitude. This data attribute is provided 
by the protocol to declare the geographical position of the device in WGS84 coordinates -latitude. Negative values 
indicate a southern latitude. WGS refers to the world geodetic system, which is used in global positioning systems (GPS), 
and 84 is the current version of the standard.
Longitude
Range: -180.000 to 180.000 degrees in steps of 0.001 degree
Default: 0.000 deg
The value entered sets the value of the data attribute <LDName>/LPHD1.PhyNam.longitude. This data attribute is 
provided by the protocol to declare the geographical position of the device in WGS84 coordinates -longitude. Negative 
values indicate a western longitude.
Altitude
Range: 0 to 10,0000 m in steps of 1 m
Default: 0 m
The value entered sets the value of the data attribute <LDName>/LPHD1.PhyNam.altitude. This data attribute is provided 
by the protocol to declare the geographical position of the device in WGS84 coordinates - altitude.
Prefix for GGIO1
Range: 0 to 11 VisibleString characters
Default: 
This setting sets the LN Prefix of the FlexLogic operand interface logical node GGIO1 that is described in the GGIO1 
section later. Valid characters are upper and lowercase letters, digits, and the underscore (_) character. The first 
character must be a letter. UR Setup software does not allow entry of a prefix that duplicates any other GGIO1 prefix 
that is used by the product, such as ConIn and ConOut.
Prefix for GGIO2
Range: 0 to 11 VisibleString characters
Default: 
This setting sets the LN Prefix of the Virtual Inputs Interface logical node GGIO2 that is described in the GGIO2 section 
later. Valid characters are upper and lowercase letters, digits, and the underscore (_) character. The first character must 
be a letter. UR Setup software does not allow entry of a prefix that duplicates any other GGIO2 prefix that is used by the 
product.
Prefix for GGIO4
Range: 0 to 11 VisibleString characters
Default: 
This setting sets the LN Prefix of the FlexAnalog operand interface logical node GGIO4 that is described in the GGIO4 
section later. Valid characters are upper and lowercase letters, digits, and the underscore (_) character. The first 
character must be a letter. UR Setup software does not allow entry of a prefix that duplicates any other GGIO4 prefix 
that is used by the product.
LLN0.Mod.ctlModel
Range: status-only, direct-with-normal-security, sbo-with-normal-security
Default: sbo-with-normal-security
This setting specifies the control service that clients must use to control the TEST MODE FUNCTION of the F35. An "on" 
control to <LDName>/LLN0.Mod changes TEST MODE FUNCTION to Disabled, an "on-blocked" control changes it to 
Forcible, and a "test/blocked" changes it to Isolated.