5-142 F35 MULTIPLE FEEDER PROTECTION SYSTEM – INSTRUCTION MANUAL
PRODUCT SETUP CHAPTER 5: SETTINGS
5
The binary input points are sent as Class 1 data. They are sent either as a response to a general interrogation received
from the controller or reported spontaneously. Spontaneous transmission occurs as a response to cyclic Class 2 requests.
If the F35 wants to transmit Class 1 data at that time, it demands access for Class 1 data transmission (ACD=1 in the
control field of the response).
For any change to take effect, restart the relay.
SETTINGS PRODUCT SETUP  COMMUNICATIONS  IEC 60870-5-103  IEC103 INPUTS MEASURANDS
IEC103 INPUTS
MEASURANDS
ASDU 1
See below
ASDU 4
ASDU 1
ASDU 1 TYP:
9
Range: 3 or 9
ASDU 1 FUN:
0
Range: 0 to 255 in steps of 1
ASDU 1 INF:
0
Range: 0 to 255 in steps of 1
ASDU 1 SCAN TOUT:
0
Range: 0 to 1000 s in steps of 1
ASDU 1 ANALOG 1
Off
Range: FlexAnalog parameter
ASDU 1 ANALOG 1
FACTOR: 1.000
Range: 0.000 to 65.535 in steps of 0.001
ASDU 1 ANALOG 1
OFFSET: 0
Range: -32768 to 32767 in steps of 1
ASDU 1 ANALOG 9
Off
Range: FlexAnalog parameter
ASDU 1 ANALOG 9
FACTOR: 1.000
Range: 0.000 to 65.535 in steps of 0.001
ASDU 1 ANALOG 9
OFFSET: 0
Range: -32768 to 32767 in steps of 1
ASDU 4
ASDU 4 TYP:
9
Range: 3 or 9
ASDU 4 FUN:
0
Range: 0 to 255 in steps of 1
ASDU 4 INF:
0
Range: 0 to 255 in steps of 1
ASDU 4 SCAN TOUT:
0
Range: 0 to 1000 s in steps of 1
ASDU 4 ANALOG 1
Off
Range: FlexAnalog parameter
ASDU 4 ANALOG 1
FACTOR: 1.000
Range: 0.000 to 65.535 in steps of 0.001